Page 2 of 2 FirstFirst 12
Results 14 to 26 of 26

Thread: Scroll or TXV

  1. #14
    Join Date
    Feb 2004
    Location
    British Columbia, Canada
    Posts
    579
    Post Likes
    Did you look at the evap coils? Low charge sometimes causes bottom 1/3 of coil to ice up or run colder and accumulate pre-icing condensation more than the upper 2/3 of the coil.
    What's your SH, SC, and amp draw?
    I'm thinking one if not two problems.
    1 - low charge
    2 - txv powerhead dead, and possible low charge if icing present

  2. #15
    Join Date
    Feb 2004
    Location
    British Columbia, Canada
    Posts
    579
    Post Likes
    Re-read your post and am thinking LOW CHARGE.
    SH, SC, Amp draw, rated load amps and locked rotor amps would be good to see.
    (LRA divided by 6 can give you close to actual normal operating amperage)

  3. #16
    Join Date
    Sep 2008
    Location
    SouthEastern Wisconsin
    Posts
    164
    Post Likes
    What are the people like in New Zealand?
    Normal is just a setting on the washing machine...

  4. #17
    Join Date
    Dec 2011
    Location
    New Zealand
    Posts
    2,723
    Post Likes
    Quote Originally Posted by nuclear rabbit View Post
    What are the people like in New Zealand?
    Liberal/lateral thinkers
    British type sense of humor
    Not to flashy
    Sports mad.
    Adventitious

  5. #18
    Join Date
    Sep 2008
    Location
    SouthEastern Wisconsin
    Posts
    164
    Post Likes
    Cool, Thanks for the Reply...
    Normal is just a setting on the washing machine...

  6. #19
    Join Date
    Sep 2008
    Location
    SouthEastern Wisconsin
    Posts
    164
    Post Likes
    It's on my list of places to see.
    Normal is just a setting on the washing machine...

  7. #20
    Join Date
    Nov 2007
    Location
    Mississippi
    Posts
    1,534
    Post Likes
    If you are unsure of the charge, why don't you just weigh it out. You said it only holds 6 lbs right? If you have 8 lbs (6 factory charge + the 2 you added), replace power element and liquid line drier. I'll bet you are just low on refrigerant.

  8. #21
    Join Date
    Jan 2010
    Posts
    12,748
    Post Likes
    Thread Starter
    Quote Originally Posted by socotech View Post
    If you are unsure of the charge, why don't you just weigh it out. You said it only holds 6 lbs right? If you have 8 lbs (6 factory charge + the 2 you added), replace power element and liquid line drier. I'll bet you are just low on refrigerant.
    Ya I think I will add 2 more pounds and see what gives. If nothing then I will be going at the power element first or I mean second after I pull charge. Lennox is telling me I have to sweet in a new valve but it looked like the power element was removable. If it is then I will just switch out the guts.

  9. #22
    Join Date
    Oct 2001
    Posts
    6,966
    Post Likes
    capillary is snapped and or the power head is shot on charge....the scroll NULLs out if there is no freon coming into the scroll.if the power head is a screw off type your into a quick fix if it is all one TXV..bring a radio up on the roof and your lunch
    "when in doubt...jump it out" http://www.youtube.com/watch?v=U1qEZHhJubY

  10. #23
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,674
    Post Likes
    I had a similar one, well, I didn't work on it, a fellow tech called me for support on it...

    He wanted to replace the compressor as well. No cool, low suction and low head.

    I told him to pull the charge and weigh it. He had almost a double charge in that one AC circuit.

    Your pump is OK. TXV or charge. SC would tell the tale, really.

  11. #24
    Join Date
    Sep 2003
    Location
    Western PA
    Posts
    1,535
    Post Likes
    I had similiar problem 2 weeks ago. I ordered a new powerhead and valve. When the parts came in, the Boss sent out another Tech. I don't know how it turned out.
    Local 449?

  12. #25
    Join Date
    Jan 2010
    Posts
    12,748
    Post Likes
    Thread Starter

    NEWS FLASH

    and now the rest of the store !

    Today I went back to the RTU. Went armed with a new OEM txv. I had made up my mind to just pull the charge to see where the numbers would come in at. Hit zero on both sides of gage at 7 pds. 6oz. So now we know it was not that much under charged. Name plate at 6 pds I added 2 last trip. Next I went right to the txv. Pulled sensing bulb, txv and equalizer line out of suction line. Power element was not removable so no quick fix. Also had to work behind the blower I added about 2 inches to the txv outlet so I would not cook the new valve. Only had about a 1 inch stub and it had to be welded to a solid brass distributor. I got that in with some nitro flowing. Pressure tested to 150 psig and so far so good. Moved over to the compressor section and replaced filter. Pressure tested once more pulled vac and put back 6 pd charge. Ambient was about 80* and gage read 250 hi side 75 low side.

    Thanks everyone for your
    Oh and that old txv I could not blow thru and the filter not much better.

  13. #26
    Join Date
    Sep 2003
    Location
    Western PA
    Posts
    1,535
    Post Likes
    Quote Originally Posted by VTP99 View Post
    and now the rest of the store !

    Today I went back to the RTU. Went armed with a new OEM txv. I had made up my mind to just pull the charge to see where the numbers would come in at. Hit zero on both sides of gage at 7 pds. 6oz. So now we know it was not that much under charged. Name plate at 6 pds I added 2 last trip. Next I went right to the txv. Pulled sensing bulb, txv and equalizer line out of suction line. Power element was not removable so no quick fix. Also had to work behind the blower I added about 2 inches to the txv outlet so I would not cook the new valve. Only had about a 1 inch stub and it had to be welded to a solid brass distributor. I got that in with some nitro flowing. Pressure tested to 150 psig and so far so good. Moved over to the compressor section and replaced filter. Pressure tested once more pulled vac and put back 6 pd charge. Ambient was about 80* and gage read 250 hi side 75 low side.


    Thanks everyone for your
    Oh and that old txv I could not blow thru and the filter not much better.
    thanks for the update.