Yeah, I know about those types of heaters. That's what was there when I started on this issue. In fact, I have a kit of various lengths of 120V braided heat cable that was given to me by one of the maintenance guys when I started work here. I thought about using them, but I ordered a RayChem 120V 12' heat cable with a NEMA 5-15 plug from Grainger. I re-piped the drain today and tapped into the light circuit on top of the box. Ran it in liquid tight conduit, mounted an indoor/outdoor 1-gang rectangle box up behind the evaporator coil so no one can mess with it and installed a receptacle cover enclosure.
Question. Where would you get 240V power all the time from the terminal block in the evaporator coil? As I said, I can get it between "N" and "3" when it's in defrost or I can get it between "N" and "4" when the fans are running, but there is no non-switched, all the time, 240V circuit at the terminal board. I would need to pull another wire from the condensing unit on the roof, which would have been a lot more trouble than installing a receptacle behind the evaporator coil.
Anyway, thanks for all the advice and suggestions everyone. I really appreciate it.
Exactly!With your chrome heart shining in the sun, long may you run.
-
04-26-2012, 05:55 PM #15
-
04-26-2012, 06:25 PM #16
-
04-26-2012, 06:30 PM #17
Member
- Join Date
- Jun 2003
- Location
- Virginia
- Posts
- 376
I have never had a problem using terminal 4 on the coil terminal board.
Also, when installing an outlet inside the box, make sure you seal the wires inside the conduit just outside the box.
-
04-26-2012, 07:58 PM #18
If you saw the end of the coil with the controls and wiring, and the conditions I'd have to do that under, you'd understand why that's impossible to do. It would be easier to pull another wire.
It remains to be seen if the receptacle will will sense a path to ground and trip. I don't think that will happen. It will not get knocked out from employees stacking boxes. It's high up, behind the evaporator coil where boxes cannot be stacked. Repiping what, the drain? What makes you say that?Last edited by SandShark; 04-26-2012 at 08:13 PM.
With your chrome heart shining in the sun, long may you run.
-
04-26-2012, 08:03 PM #19
Regular Guest
- Join Date
- Sep 2011
- Location
- Plainfield IL
- Posts
- 101
I recommend not putting a GFI outlet inside the freezer unless you enjoy working on frozen drain lines! I also highly recommend using a trap because if you don't you will get snow build up in drain opening. Best of luck. In freezers I like to use Tee's with cleanouts instead of elbows....then when the drain line freezes over all I have to do to clear out the ice is heat up a piece of threaded rod and shove it thru the drain.
-
04-26-2012, 08:37 PM #20
Yeah, I've been warned multiple times now not to use a GFCI, but I appreciate your repeating that warning. I think I get it. Trap has been installed, but thanks for the tip. Heat up a piece of threaded rod, huh? I'll have to write that one down so I don't forget. Thanks!
With your chrome heart shining in the sun, long may you run.
-
04-26-2012, 10:14 PM #21
Regular Guest
- Join Date
- Oct 2008
- Location
- mid-Tennessee
- Posts
- 272
I'm all for a dedicated circuit. Once wires are run inside the conduit, squirt a generous glob of silicone up in it to prevent the vacuum of sub-zero temps pulling air and moisture through it and to your outlet box. Otherwise, the box will build a nice ice cube in it.
Raychem, like Frostex, is hundreds of little parallel heaters. I've never had to remove a Raychem due to failure. I have always used insulation with it to be sure. Frozen condensate lines create a real mess and uninsulated pipe or failed sub-standard heater tape was always the culprit. Allotta work to fix it, so do it with the best stuff you can find this time around.
Oh yes!
Noo-o-o-o GFCI!
-
04-26-2012, 10:26 PM #22
Professional Member
- Join Date
- Apr 2012
- Location
- Jackson, MS
- Posts
- 29
I've always thought it looked a lot neater coming out of a junction box on the light circut or dedicated and I've always added a pigtail butt connectors and heat shrink to extend the line to the box or the electrical panel on the evaporator.
-
04-27-2012, 08:07 AM #23
A thought.
Wire the light circut to the load side of the gfi.
It trips, no lights, they should call about no lights in the box.
Of course they might not care and won't call until the door is frozen shut.
-
04-27-2012, 02:23 PM #24
Agreed. While I see allot of 120volt receptacles they have already been installed (by and electrician). If there is not one then definitely N and 4 with the 240 volt heater. Make sure you get all the ice out of the line and fix the splits. Then wrap it up and insulate
Sent from my amazing 4G device
-
04-27-2012, 07:00 PM #25
-
04-27-2012, 07:05 PM #26
Regular Guest
- Join Date
- Sep 2011
- Location
- Plainfield IL
- Posts
- 101
Beautiful job. I see plenty of pitch on your pipe....Looks nice!