    converting cap tube to TXV

    Ive read of guys converting cap tubes to TXV's in reach ins, Any body do this regularly, does it pay off in the long run from clogging cap tubes in POE systems. Don't you need a reciever or large enough condensor to hold excess liquid? how would you figure out the tonnage of a box? I'm buying a problematic TRUE TSSU-27 second clogged cap tube. Customer wants to get a new one, so I'm buying it off him. I was gonna change the oil in comp. and maybee make a project out of it and put in a TXV. If it can be done, how would you size it properly? can I just take the BTU rating of the compresser?

  2. #2
    Join Date
    Oct 2002
    Posts
    1,350
    It will work. I larger cond. coil or receiver may be needed, but try just TXV first. Compressor with TXV usually has a higher starting torque rating.

    Add a sight glass if you use a non-glide refrigerant will help see what's going on.

  3. #3
    Join Date
    Mar 2007
    Location
    wedged in freezer shelf
    Posts
    6,980
    I just changed a pump on one and the cap tube and strainer were plugged very badly.
    Whatever the size was I went with two feet less.
    You may have a problem starting if the pressures don't equalize like they do with a cap tube.
    I don't think POE/Captubes are completely at fault for all of this since I've seen plenty of units with completely blocked condensers that were never cleaned since the original purchase and the cap tube made it through fine.
    I wouldn't bother with a TXV on that one. If it was mine I would put in a different size cap tube
    “If You Can Dodge A Wrench You Can Dodge A Ball”

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event