    question about mini-split system

    I recently got a quote on installing a mitsubishi mini split system. I was interested in installing a heat pump system to cool and heat some areas of my home. I have a 2 story colonial style house and from doing some research, I learned that I could condition up to 4 areas or rooms in my house using one outdoor unit and indoor blower in each area.

    The salesman from a recommended company comes out and says I can only have one indoor blower per outside compressor. I then get a quote of two MUZFE12NA 23 SEER outdoor condenser/heat pump units and two Mitsubishi model MSFE12NA indoor blowers. This is to condition my lower level.

    The salesman said I would need the same amount of equipment to condition my second floor, doubling the price.

    Does this sound correct or am I getting bad info from someone trying to take me to the cleaners?

  2. #2
    Join Date
    May 2008
    Location
    Missouri
    Posts
    3,565
    You can do multiple indoor units with one outside condensor. I'd call another company and have them come out. We installed 3 indoor evap units on one condenser a few years ago, and they work fine. I think they were Diaken units, but not sure. Call another company as you're not getting the real story!

  3. #3
    Join Date
    Sep 2007
    Location
    Boise, ID
    Posts
    4,326
    Diakin, LG, Sanyo, Mitsubishi, they all have models that will do multiple indoor units off of one outdoor unit. Not sure about the models you listed but a quick visit to their web site would answer your question.
    If a nation expects to be ignorant and free, in a state of civilization, it expects what will never be. (Thomas Jefferson 1816)

  4. #4
    Thanks for your replies! I just called another company and they confirmed what you said. They will be coming out to give me an estimate.

  5. #5
    Just one more quick question if I could. At what temp do these units become ineffective or innefficient for heating? I have read that they can provide heat down to approx. 15 degrees F.

  6. #6
    Join Date
    May 2008
    Location
    Missouri
    Posts
    3,565
    Different for each brand and whether or not they have built in strip heat. Make sure and discuss this with sales folks prior to purchase.

  7. #7
    Join Date
    Feb 2010
    Location
    In a boiler room
    Posts
    7,157
    Quote Originally Posted by Paul Clinton View Post
    Just one more quick question if I could. At what temp do these units become ineffective or innefficient for heating? I have read that they can provide heat down to approx. 15 degrees F.
    The units you were quoted are Hyper Heat models which have full rated heating output down to 5 outdoor temp. Even below zero they still heat, the output is less than

    Non Hyper heat models start dropping off at 20 - 30 and are down to very little heat at 0.

    None of the Mitsubishi models have built in strip heat.

    The limiting factor for using multiple indoor heads is the lineset lengths. Example; the MXZ-4A36 can only have a total connected line length of 230 ft with a max of 82 ft for any individual indoor head. There are limits to height difference too.

  8. #8
    Thanks for your help wahoo and chuckcrj.
    I have a guy from another company coming our Friday. It seems the Mitsubishi systems are popular in this area. In fact, they're the only systems I have seen in this area.

    I have electric radiant heat in the ceilings in my house, which I actually like a lot. Very comfortible and mcuh cheaper than oil. When the temp gets too low i can still use that.

  9. #9
    Join Date
    Feb 2009
    Location
    Portland OR
    Posts
    2,001
    Paul, where are you located as this is a big climate factor in system selection and sizing. Also do you plan on keeping the ceiling heat as a backup or just using the ductless?

    Any Mitsubishi with a model number MXZ is a multi(X) zone(Z) system, they came in two, three, four and eight port units.
    Check out my YouTube channel - http://www.youtube.com/user/skyheating1 We have customer testimonials, product reviews and more!
    Like us on FACEBOOK if you like our advice here!

  10. #10
    Join Date
    Aug 2004
    Location
    North Richland Hills, Texas
    Posts
    14,915
    Depending on the total capacity involved, it may be worth stepping up to the next level from the multisplit units to a full blown VRF system.

    Mitsubishi City Multi S-Series
    http://www.mitsubishipro.com/media/226453/cmcatalog.pdf

    Daikin VRVIII-S
    http://www.daikinac.com/residential/...oducts&page=55
    If more government is the answer, then it's a really stupid question.

  11. #11
    I'm located in central Massachusetts.
    I do plan on using the ceiling radiant heat i currently have as I'm not sure I can reach everywhere in my house with the mini split system.