    Placement of ID TXV bulb - how critical?

    Instructions say it should be installed on a horizontal run of the vapor line, near the equalizer line. If bulb installation is made on a vertical run, the bulb should be located at least 16 inches from any bend ,and on the tubing sides opposite the bend.

    Mine has been installed on the vertical run just past the bend, and before the multi branching of the vapor line to the coil.

    Obviuosly not 16 inches from any bend...

    York Affinity with matched York coil.

  2. #2
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    20,892

  3. #3
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    62,165
    Quote Originally Posted by jpsmith1cm View Post
    It is secure and well insulated?
    If so, its works fine there.
    Contractor locator map

    How many times must one fix something before it is fixed?

  4. #4
    Join Date
    Jul 2008
    Location
    Alabama
    Posts
    658
    My Trane units I install have the bulb right at the bend before the suction line comes out.
    I serviced a Gooooman unit the other day and their txv bulb is outside the cabinet. Insulated of course.

    As long as its insulated from any ambient attic air you can put it anywhere on the suction.
    You're only as good as your customer will allow you to be.........If they want junk, sell them junk, but make your junk look neat!!!

  5. #5
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    20,892

  6. #6
    Join Date
    Jan 2004
    Location
    Lancaster PA
    Posts
    62,165
    EZE2489, this is the Ask Our Pro's forum, and only Pro members that have been vetted by the AOPC may post advise here. Please apply to the AOPC today, thank you.

    You can find the rules for posting and qualifications here.

    Further infractions may result in loss of posting privileges.
    Contractor locator map

    How many times must one fix something before it is fixed?

  7. #7
    Join Date
    Jun 2005
    Location
    SW Wisconsin
    Posts
    3,677
    If mounted vertically, make sure the power element cap tube is "up" on top of the power element, not on the bottom.

    The power element is best mounted on the suction line near where the external equalizer measures the pressure drop over the evaporator coil back to the TXV.

    When mounted horizontally, they're usually mounted tightly on a cleaned tubing surface at 10 or 2 o clock positions.

    As critical as mounting is; it is equally important to run all the checks to see if the TXV is functioning properly & there are no restrictions anywhere, including the external equalizer.
    Last edited by udarrell; 04-22-2012 at 03:10 PM. Reason: equally important to run all the checks to see if the TXV is functioning properly

  8. #8
    Join Date
    Mar 2012
    Posts
    35
    Quote Originally Posted by superd77 View Post
    My Trane units I install have the bulb right at the bend before the suction line comes out.
    If your bulb is horizontal, that is exactly where York recommends to install the bulb. Bends are not an issue, that way. It would be near the equalizer line also, on a York coil like mine.

    The guys told me it's fine where mine is (vertical, past the bend), as long as it's secured and insulated. Which it is. Thank you for that, you guys. Much appreciated.

    I'm then trying to understand why York would say to put it at least 16 inches from any bend (when vertical),and on the tubing sides opposite the bend.

  9. #9
    Join Date
    Mar 2012
    Posts
    35
    Quote Originally Posted by udarrell View Post
    If mounted vertically, make sure the power element cap tube is "up" on top of the power element, not on the bottom.
    It is.

    Quote Originally Posted by udarrell View Post
    The power element is best mounted on the suction line near where the external equalizer measures the pressure drop over the evaporator coil back to the TXV.
    That is what York recommends as well.

    Quote Originally Posted by udarrell View Post
    As critical as mounting is; it is equally important to run all the checks to see if the TXV is functioning properly & there are no restrictions anywhere, including the external equalizer.
    They did not check the valve itself, but the temps while heating.