Results 1 to 13 of 22
    Jul 2009
    460v to 24v transformer tripping
    The 460v to 24v 4amp transformer overload keeps tripping about every 4 hours. Unit is a dx system. Any ideas why. Thanks
    Apr 2011
    could be many things but I would start looking for a short in wire somewhere. Had one similar where a valve would open in a pharmaceutical plant and move the 24v and it happened to have a rip on the wire and it would trip. Took forever to find this out as the damn valve that would move was only opened and closed for a short period of time.
    Jan 2010
    Toronto,Ontario Canada
    the first thing you look at is the max fused/breaker size on unit and see if it has the correct one in. then start looking at the motors see if they are over amping then see any loose connections.. start eliminating components!
    Get er Done!
    Do what has to be done
    when it has to be done
    as well as it has to be done
    And doing it all the time.
    Oct 2009
    God's country - Shenandoah Valley, VA
    Quote Originally Posted by wika_boy View Post
    Quote Originally Posted by akelesis View Post
    Akelesis, did you read his post carefully? He said the 4 amp transformer overload keeps tripping. That overload is in the 24V circuit. What would the breaker or the motor in the 460V circuit have to do with that?
    Wika_boy, are you a DIY. An HVAC tech would know how to diagnose that.
    Southeastern Pa
    New transformer?
    Correct tap?
    Measured load on secondary?
    2 Tim 3:16-17
    AOP Forum Rules:
    once you verify correct voltage on the primary side of your xfmr id check the loads like already mentioned. you could ohm each holding coil but depending on size of system & amount of components it might take a while but it beats repeat trips to location
    SE Pennsylvania
    Measure the amp draw on the 24 volt side as the unit runs, somethings coil could be overheating then shorting or the amp draw is close to the breaker trip point that it takes that long to heat up and trip. Had an unloader coil do that a while back, unit would run a good 30 minutes.
    Feb 2012
    Upstate SC
    Quote Originally Posted by hvac69 View Post
    I've run in to the same situation with run contactors. Thank you NAFTA!
    Jan 2010
    sorry buddy. i misread the thread. i was too quick to respond. sorry guys i do look like an idiot now
    Get er Done!
    Nov 2007
    Mississippi
    I'd check the amp draw on the secondary side with all components energized. If not overamping, replace thermostat wire. Sometimes that is the quick fix.
    Oct 2010
    Austin, TX
    Check the time delay. I have seen time delays do this several times.
    If you're too "open" minded, your brains will fall out.
    Artificial intelligence is no match for natural stupidity.
    Oct 2002
    Plano, TX
    Drop a fuse on each control load. See which load is popping fuse. Y1 , G, Y2 loads.
    Dec 2011
    Kansas City
    I'm with timjimbob. Best way to start isolating the problem since it is intermittent.