Thread: nordyne system

  1. #1
    Join Date
    Jan 2008
    Location
    s chester county,pa
    Posts
    144

    nordyne system

    just got back from a call. New customer 3 year old system. Last year 1 1/2 lbs 410 was added by installing contractor, as customer says. Turn on system. Running in a vacuum, 20psi head. So charge is gone. Put 200 psi nitro and a trace of 22 in and it holds while i check every single joint in the entire system with infra detector and big blu. isolate condensor and put 450 psi in check everything again and it holds. No oil anywhere and it is holding. Left it charged with nitro gonna check it on thursday. Have there been problems with these units? I'm thinking I'm going to evac, charge and put locking caps on they are crying poor.
    Idu m#B5vm-x25k-a S#B5070414373
    Odu m#Fs4bd-024ka S#Fsd080401611

  2. #2
    Join Date
    Feb 2012
    Location
    Opelousas La.
    Posts
    90
    Does it have a micro channel coil?

  3. #3
    Join Date
    Jan 2008
    Location
    s chester county,pa
    Posts
    144
    no conventional coils in and out. My wife is from LaPlace how's the weather down their?

  4. #4
    Join Date
    Feb 2012
    Location
    Opelousas La.
    Posts
    90
    Quote Originally Posted by wogpa67 View Post
    no conventional coils in and out. My wife is from LaPlace how's the weather down their?
    Its a small world lol. The weather has been in the middle 80's for the last month or so, but it stayed pretty cool today. Just waiting on the heat.

  5. #5
    Join Date
    Jan 2008
    Location
    s chester county,pa
    Posts
    144
    We were down last april for the week those tornadoes came through. She said that's horse country. if she remembers? Like here but flat and coona$$ country

  6. #6
    Join Date
    Jan 2008
    Location
    s chester county,pa
    Posts
    144

  7. #7
    Join Date
    Feb 2012
    Location
    Opelousas La.
    Posts
    90
    Quote Originally Posted by wogpa67 View Post
    We were down last april for the week those tornadoes came through. She said that's horse country. if she remembers? Like here but flat and coona$$ country
    Yep. Plenty of horses and coona$$es around here.lol

  8. #8
    Join Date
    Feb 2006
    Location
    Float'N Vally, MS
    Posts
    1,776
    3 yrs. old, double check the inside coil. If so, call Nordyne warranty issue.
    Life is too short, Behappy!
    TFMM

  9. #9
    Join Date
    Jan 2008
    Location
    s chester county,pa
    Posts
    144
    any one else have anything? it may just be kids huffing it, but it's a nice neighboorhood and the caps were on still

  10. #10
    Join Date
    May 2000
    Location
    Indianapolis, IN, USA
    Posts
    33,396
    Never had issues with Nordyne 22, the early 410 units had ball valves for service valves that leak like crazy.

  11. #11
    Join Date
    Feb 2006
    Location
    Float'N Vally, MS
    Posts
    1,776
    Quote Originally Posted by wogpa67 View Post
    Last year 1 1/2 lbs 410 was added by installing contractor,
    Idu m#B5vm-x25k-a S#B5070414373



    Had a bunch of these BaldLoonie. I believe there was a paper on this?

    Life is too short, Behappy!
    TFMM

  12. #12
    Join Date
    Jan 2009
    Location
    Etters PA.
    Posts
    493
    Bad indoor coils along with the valves of the older units but at 3 years old it shouldn't be the valves but very likely could be the I/d coil. most of the coil leeks I found were on the inner part of the coil not on the u bends.

    Sent from my PC36100 using Tapatalk 2

  13. #13
    Join Date
    Apr 2012
    Location
    Pasadena,Maryland
    Posts
    265
    I would say use a micron gauge when you evacuate,if it holds 500 micron than I would say your safe to recharge, btw I never heard of anyone putting in a trace of r22 in a 410 system.is that an acceptable practice. Just wondering.

Page 1 of 3 123 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event