Knocking noise in system
We are looking at a Rheem system, heat pump. When it cycles off it begins a knocking sound after approx 3 min. Goes for 60-90 sec, slows down and then stops. It sounds like metal on metal. We have some ideas but are looking for input.
-
04-17-2012, 03:25 PM #2
New Guest
- Join Date
- Feb 2012
- Location
- Alabama
- Posts
- 5
Need model # and serial # of unit.
where is the noise coming from?
-
04-18-2012, 07:43 AM #3
Professional Member*
- Join Date
- Oct 2002
- Posts
- 675
How long is lineset and evap and condenser same elevation?
-
04-18-2012, 09:00 AM #4
Professional Member
- Join Date
- Oct 2005
- Location
- Atlanta GA
- Posts
- 30
Same issue last week on a Weather King (Rheem). Knocking was at outdoor TXV after shut down. All operating values were normal. This being an investment property with the owners wanting "the cheapest fix", installed a solenoid valve in the liquid line. Problem was solved.
-
04-18-2012, 09:22 AM #5
Professional Member*
- Join Date
- Oct 2002
- Posts
- 675
TXV=$70, Solenoid= $120. Cheaper? Guess less labor on Solenoid.
-
04-18-2012, 12:44 PM #6
Rheem knows about it. Likely will need a bleed type TXV put in the outdoor unit. Even then, might not stop it. We're 1 out of 2. I'll ask our tech rep about the solenoid idea.