    Temp control question

    Something has been bugging me that I just can't understand, and my textbooks don't seem to address it. It may be a dumb question...

    Lets say we have a case that we want to keep at 38 degrees. Let's also assume we have an R-22 rack system where the suction setpoint is at 53 psig (which would give an evap temp of 28). But, let's say the manager of the department wants the case to be a freezer (it's farfetched, but it's for illustration). There's no way you can lower the suction setpoint to get 0 degree case temp, of course, because all the other circuits need medium temp suction pressure.

    Here's my question...even with the evaporator temp at 28 degrees due to the suction sp at 53 psig, if you just kept the solenoid open feeding the case with refrigerant constantly, couldn't you take it down to the required 0 degrees? Why not? Would the coils ice up? I know this isn't *normally* done, but I need to understand the "why" of it...

  2. #2
    Join Date
    Mar 2004
    Location
    Las Vegas, Nevada
    Posts
    1,648
    Post Likes
    Think of your evaporator temp as the basement. There is no way you can chill your equipment or box or whatever to a temperature lower than your evaporator. Not in this reality.
    The views and opinions posted here are my own. They do not reflect the corporate policies of my employer and will most likely get me fired at some point.

  3. #3
    Join Date
    Feb 2008
    Location
    California
    Posts
    2,091
    Post Likes
    Quote Originally Posted by Iceneck View Post

    Here's my question...even with the evaporator temp at 28 degrees. if you just kept the solenoid open feeding the case with refrigerant constantly, couldn't you take it down to the required 0 degrees? Why not? Would the coils ice up? I know this isn't *normally* done, but I need to understand the "why" of it...
    If you figure out a way to take a 28* evap coil and produce a 0* case...you have defeated the science behind physics and have redefined thermodynamics.

    Start thinking about refrigeration as a heat transfer process and this should become clear to you.

    Heat travels from hot to cold...at least on this planet. (heat transfer should be covered in your textbook within the first few chapters)

  4. #4
    Join Date
    May 2011
    Location
    CA
    Posts
    123
    Post Likes
    Thread Starter
    Heat transfer is the way I do think of it (when the refrigerant vaporizes, it takes in heat, and when it condenses, the heat is removed) but I thought...ahh, I don't know what I was thinking. I was thinking the heat would keep "going into" the refrigerant if the process was still occuring (i.e. more refrigerant was being fed into the evaporator).

    So, just for kicks...if one really wanted to turn one case on MT rack into a frozen case, you could lower the entire rack suction pressure to get 0 degrees evap temp for that case...and then put an epr on all the other cases to raise the evap temp? I know this would never be done, but it *could* be, right? Theoretically?

  5. #5
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    Quote Originally Posted by Iceneck
    Heat transfer is the way I do think of it (when the refrigerant vaporizes, it takes in heat, and when it condenses, the heat is removed) but I thought...ahh, I don't know what I was thinking. I was thinking the heat would keep "going into" the refrigerant if the process was still occuring (i.e. more refrigerant was being fed into the evaporator).

    So, just for kicks...if one really wanted to turn one case on MT rack into a frozen case, you could lower the entire rack suction pressure to get 0 degrees evap temp for that case...and then put an epr on all the other cases to raise the evap temp? I know this would never be done, but it *could* be, right? Theoretically?
    Until you blow the compressors up from running them outside design limits....

    Sure, though, theoretically, it will work.



  6. #6
    Join Date
    Feb 2008
    Location
    California
    Posts
    2,091
    Post Likes
    If you wanted to choose the most expensive and time consuming way possible...

    sure why not, that would work.

  7. #7
    Join Date
    Feb 2008
    Location
    California
    Posts
    2,091
    Post Likes
    Quote Originally Posted by Iceneck View Post
    Here's my question...even with the evaporator temp at 28 degrees due to the suction sp at 53 psig, if you just kept the solenoid open feeding the case with refrigerant constantly, couldn't you take it down to the required 0 degrees? Why not? Would the coils ice up? I know this isn't *normally* done, but I need to understand the "why" of it...
    couldn't you take it down to the required 0 degrees? No

    Why not? Heat transfers hot to cold. For heat to transfer, there must be a thermal difference between 2 objects. If the evaporator is at 28*, at BEST it could only absorb heat until a 28* equilibrium is reached. at which point no further heat transfer takes place...it is physically impossible for a 28* evaporator to lower the temperature of any medium below 28*. YOU MUST UNDERSTAND THAT

    Would the coils ice up? Yes

    I hope this helps you understand the "why".

    It's important to think things through logically. cause & effect. This stuff is 100% basic physics principles. NO magical devices. Things don't just happen Willy-Nilly.

    understanding the principles is one thing, then you have to be mechanically inclined enough to do the physical work, and that's a whole other game.

  8. #8
    Join Date
    May 2011
    Location
    CA
    Posts
    123
    Post Likes
    Thread Starter
    Quote Originally Posted by Phase Loss View Post
    couldn't you take it down to the required 0 degrees? No

    Why not? Heat transfers hot to cold. For heat to transfer, there must be a thermal difference between 2 objects. If the evaporator is at 28*, at BEST it could only absorb heat until a 28* equilibrium is reached. at which point no further heat transfer takes place...it is physically impossible for a 28* evaporator to lower the temperature of any medium below 28*. YOU MUST UNDERSTAND THAT

    Would the coils ice up? Yes

    I hope this helps you understand the "why".

    It's important to think things through logically. cause & effect. This stuff is 100% basic physics principles. NO magical devices. Things don't just happen Willy-Nilly.

    understanding the principles is one thing, then you have to be mechanically inclined enough to do the physical work, and that's a whole other game.
    Got it! Thanks....

  9. #9
    Join Date
    Mar 2004
    Location
    Las Vegas, Nevada
    Posts
    1,648
    Post Likes
    Quote Originally Posted by Iceneck View Post
    So, just for kicks...if one really wanted to turn one case on MT rack into a frozen case, you could lower the entire rack suction pressure to get 0 degrees evap temp for that case...and then put an epr on all the other cases to raise the evap temp? I know this would never be done, but it *could* be, right? Theoretically?
    There is any number of island coffin-case line-ups at the larger membership stores that do just this. They typically have a switch at the rack that bypasses the epr. They've proven to be the service guy's pita. But the stores like them for seasonal promotions such as turkeys during Thanksgiving. Yes, it can be done.
    The views and opinions posted here are my own. They do not reflect the corporate policies of my employer and will most likely get me fired at some point.

  10. #10
    Join Date
    Feb 2008
    Location
    California
    Posts
    2,091
    Post Likes
    It can be done...

    But we must agree that dropping the MT suction setpoint to achieve a 0* case temperature is NOT the ideal way to do this...?

    We are talking about running the compressors out of their operating envelopes AND installing EPR's on all other MT cases on that Rack that are not going to run as a freezer....this would be costly and insane.

    There is a better way to setup Dual Temp cases.

  11. #11
    Join Date
    May 2011
    Location
    CA
    Posts
    123
    Post Likes
    Thread Starter
    Quote Originally Posted by Phase Loss View Post

    There is a better way to setup Dual Temp cases.
    Split suction, right?

  12. #12
    Join Date
    Feb 2008
    Location
    California
    Posts
    2,091
    Post Likes
    Quote Originally Posted by Iceneck View Post
    Split suction, right?
    nope

    I'd imagine you could divert the suction to either a MT or LT split suction header with a Valve...just never seen that.

    There's an even simpler way.

  13. #13
    Join Date
    Sep 2005
    Location
    florida
    Posts
    5,520
    Post Likes
    Quote Originally Posted by engineerdave View Post
    There is any number of island coffin-case line-ups at the larger membership stores that do just this. They typically have a switch at the rack that bypasses the epr. They've proven to be the service guy's pita. But the stores like them for seasonal promotions such as turkeys during Thanksgiving. Yes, it can be done.


    Yes but those are on LT racks.
    I love the smell of phosgene first thing in the morning:

    To apply for professional membership click here


    Educational forums are open.

    If you would like to submit a link or an article or other related info to the EF. click here

  14. #14
    Join Date
    Mar 2004
    Location
    Las Vegas, Nevada
    Posts
    1,648
    Post Likes
    Quote Originally Posted by crackertech View Post
    Yes but those are on LT racks.

    Absolutely. And as some of you guys have pointed out, I'm not convinced the utility bill is happier as a result.
    The views and opinions posted here are my own. They do not reflect the corporate policies of my employer and will most likely get me fired at some point.

  15. #15
    Join Date
    Sep 2005
    Location
    florida
    Posts
    5,520
    Post Likes
    Quote Originally Posted by engineerdave View Post
    Absolutely. And as some of you guys have pointed out, I'm not convinced the utility bill is happier as a result.


    But the op wanted to take a MT case and pump and turn it into a freezer.Nope it cant be done.
    I love the smell of phosgene first thing in the morning:

    To apply for professional membership click here


    Educational forums are open.

    If you would like to submit a link or an article or other related info to the EF. click here

  16. #16
    Join Date
    Feb 2008
    Location
    California
    Posts
    2,091
    Post Likes
    Cracker spilled the beans.

    The way to do dual temp is pipe the case to the LT rack. Then install a EPR with bypass or some other form of bypass. You will also need a means of defrost for LT mode. Whether it be gas or electric.

  17. #17
    Join Date
    Sep 2005
    Location
    florida
    Posts
    5,520
    Post Likes
    Quote Originally Posted by Phase Loss View Post
    Cracker spilled the beans.

    The way to do dual temp is pipe the case to the LT rack. Then install a EPR with bypass or some other form of bypass. You will also need a means of defrost for LT mode. Whether it be gas or electric.


    I got's more beans some were.
    I love the smell of phosgene first thing in the morning:

    To apply for professional membership click here


    Educational forums are open.

    If you would like to submit a link or an article or other related info to the EF. click here

  18. #18
    Join Date
    Dec 2010
    Location
    Virginia
    Posts
    360
    Post Likes
    What does MT and LT stand for? Not a rack guy and have never heard the terms.

  19. #19
    Join Date
    Sep 2005
    Location
    florida
    Posts
    5,520
    Post Likes
    Quote Originally Posted by millertime77 View Post
    What does MT and LT stand for? Not a rack guy and have never heard the terms.

    It's not rack talk per say Mt= Medium temp LT= low temp.
    I love the smell of phosgene first thing in the morning:

    To apply for professional membership click here


    Educational forums are open.

    If you would like to submit a link or an article or other related info to the EF. click here

  20. #20
    Join Date
    Dec 2010
    Location
    Virginia
    Posts
    360
    Post Likes
    thanks for clearing that up for me, I kind of thought thats what it was.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •