    Quote Originally Posted by tcy612 View Post
    I agree with you Rob... Next to the economizer gaskets, the biggest source of leaks is (ironically) the place where the non-condensables are supposed to be removed.
    The new flange kits are definitely the fix for those things. On smaller ones with 4 bolts, I've had some success drilling and tapping the additional 4 holes. Even on the 8 bolt and 12 flanges, if you are meticulous with your installation and pay attention to the details, they're not problems anymore.
    The key to happiness is lower expectations.

  2. #15
    Join Date
    Aug 2009
    Location
    Prattville, Alabama
    Posts
    2,140
    Quote Originally Posted by Tech Rob View Post
    The purge is the lowest common denominator. It's a whole lot cheaper and easier to fix than pressurizing the chiller and leak testing. There's a short list of things that I always check on every one before I go and pressurize the machine for a leak test.
    I agree, Rob. The Purge is key to the chiller. I would always do a quick run test and inspection of it on all service calls I went on, even if the call was not purge or head pressure related. Sometimes I would find extra work. More than once I found "Max pump-out rate exceeded" that was a month or more old and still active (not ever reset).

Page 2 of 2 FirstFirst 12

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event