Results 1 to 8 of 8
    Apr 2012
    TOTAL HR AIR COOLED CHILLERS
    hello
    does some one know about EWT to heat recovery heat exchangers using R-134a?
    in a project i deal with the chileer IOM say that the min enetring water temp is 28C.
    and that a BYPASSS VALAVE is needed.
    can someone give some more info ?
    rgrds
    rony
    Moved to chiller forum.
    Not in Iran
    There should be a (bypass) with a balance valve between the supply and return water., the reasoning behind this is to balance the system.,
    balance can mean, as for water pressure/flow and the other more advance reason could be to (control ) water temps.,
    no signature blast'em man blast'em
    !!!KILL THE TERRORIST!!!
    Oct 2010
    Greece
    Hi,
    Most probably you have W/C and A/C condenser in series and the W/C (HR) condenser is a PHE and first in the line.
    IOM indicates this because when the compressor is not in operation and water temp is below 28C then saturation of refrigerant may occur and fill up the PHE with liquid.
    When compressor starts you may have hydraulic hammering and brake PHE.
    The configuration may be pump – PHE – 3way and pump or loads in order to raise the temperature as quick as possible.
    Hope my approach is helpful.
    Regard,
    CV
    Apr 2012
    ?! hydraulic hammering
    hi
    asuume the unit is in the first comision and water temp is 20c.
    the heat recovery water pump is "off" .
    do you think in this situation we can face the hydraulic hammering ?
    if the situation is like this how can the unit start up ?
    we dont have heat source to heat the HR water at firs start !!!
    to brake PHE at first start sound to me not so good !!!!
    rony
    Ohio
    This is NOT a Do It Yourself site.
    We get paid to solve these problems.
    Some of you pro members needs to learn this. Keep helping for nothing and this site will be overrun with people asking you to use your knowledge for free.
    Apr 2012
    hello ZW17
    you are correct .
    its my mistake to ask this question .
    rony
    Quote Originally Posted by ronydaiki View Post
    hello ZW17
    you are correct .
    rony
    No its not.
    However, some members will chose not to aid anyone that is not a Pro member. And that is there right.
    Please get your post up to 15 and apply for pro membership.
