hmmm blue vac?
how much better than say Robinair 14830A thermistor micron gauge or Supco VG64?
-
02-14-2013, 08:53 AM #67
-
02-14-2013, 04:52 PM #68
Regular Guest
- Join Date
- Nov 2004
- Location
- Western NY
- Posts
- 946
-
02-14-2013, 05:10 PM #69
Attempted to use my HB supernova this morning. The vac pump had been running over night, the supernova said I was at 2500 microns, I was 100% sure there were no leaks. Thought it might have been my pump, so I connected the supernova to just the pump, still only dropped to 2100. Got the trusty but bulky thermal vac guage out. Connected it to system.... 400 microns. This only the 4-5 time I tried to use the supernova. It might have worked properly the first time or two.