  1. #27
    Join Date
    May 2004
    Posts
    1,886
    Which Bluvac are you guys using? The Standard one or the LTE? I'm thinking about buying one, just not sure which model.

  2. #28
    Join Date
    Aug 2010
    Location
    Florida
    Posts
    251
    Quote Originally Posted by 270wsm View Post
    Which Bluvac are you guys using? The Standard one or the LTE? I'm thinking about buying one, just not sure which model.
    Hi, 270wsm.

    The BluVac and BluVac LTE are both built upon the same 'engine'. They each have the same speed and accuracy, both have the oil/calibration indicators, and can both be recalibrated to factory specs using your freezer.

    The main differences between the BluVac and LTE is that the BluVac has additional "productivity" features, including a "leak rate" indicator, an ambient temperature indicator (to 0.1 C/F), and programmability (it allow you to automate the evacuation process). In addition, the BluVac has 0.1 micron resolution below 10,000 microns, where the LTE is 1 micron resolution throughout the entire range of 0 to 25,000 microns.

    Which ever one you decide to buy, I stand by our gauges, and will help you with any problems you may encounter, to the best of my ability.

    Thanks for your interest!

  3. #29
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    25,924
    Quick question, joeyd.

    When the BluVac needs calibration, will it just quit like it does when it is oil contaminated or does it give an alert but continue to function?

  4. #30
    Join Date
    Aug 2010
    Location
    Florida
    Posts
    251
    Quote Originally Posted by jpsmith1cm View Post
    Quick question, joeyd.

    When the BluVac needs calibration, will it just quit like it does when it is oil contaminated or does it give an alert but continue to function?
    The oil sensor operates continuously, and will allow the gauge to function normally (with the OIL indicator on) until contamination becomes so extensive that proper operation cannot be guaranteed. Then the gauge gets locked out until it is cleaned.

    The calibration check must be activated manually by pressing and holding the power key during power-on (as detailed in the owner's manual). Cal GOOD means the gauge is in calibration, Cal SOON means the gauge is operative, but calibration is not guaranteed. There is no lockout for calibration.

    Slight oil contamination could make the calibration check indicate SOON. It is always a good idea to clean and dry the sensor (with alcohol, then pull a quick vacuum) prior to calibration, though this is not strictly necessary (the calibration process itself accounts for any changes in the sensor, including accumulated contamination).

  5. #31
    Join Date
    Mar 2007
    Posts
    3,136
    Quote Originally Posted by joeyd View Post
    As much as I would love to send you a freebie, Tech Rob, what would I do without my detractors keeping these threads going?

    I've actually given a number of them away over the past 2 years for evaluation purposes...and the feedback has always been superlative. But, if it's all the same, I'd like to start making some money by selling some of them! Thanks for the thought, though.
    That's ok... Your loss

    Maybe I will try the LTE one of these days. I don't need all of the other whiz-bang gimmickry. I want something that will show me a number when I hook it up and turn it on. That is all.

    I don't get the need for an oil sensor or a leak rate indicator. If the thing is held upright, and you don't apply any pressure to it, there is no way oil is ever going to get in that sensor. If I hook up the micron gauge and it says 2000 microns, I'm going to do one of three things... That is 1) change the pump oil, 2) go get another cup of coffee, 3) pressurize the system and look for a leak. It's not like I'm going to sit there looking at the leak rate indicator going "Hmm, well, even though it's at 2000 microns, the bluvac says the leak rate is 0... I guess we can go ahead and charge it!"

    No disrespect intended... Obviously you're doing something right if you've got half of this site brainwa... I mean using your gauge.

    I also want to add that I think it's very cool for you to get on this forum and interact with the folks using your tools, answering questions, and offering instantaneous support. That is very rare and quite invaluable these days!
    The key to happiness is lower expectations.

  6. #32
    Join Date
    Aug 2010
    Location
    Florida
    Posts
    251
    Quote Originally Posted by Tech Rob View Post
    That's ok... Your loss
    Maybe I will try the LTE one of these days. I don't need all of the other whiz-bang gimmickry. I want something that will show me a number when I hook it up and turn it on. That is all.
    And that is why we decided to release the LTE...there are many (most?) that don't need the features the BluVac provides.

    Quote Originally Posted by Tech Rob View Post
    I don't get the need for an oil sensor or a leak rate indicator. If the thing is held upright, and you don't apply any pressure to it, there is no way oil is ever going to get in that sensor.
    You are a careful pro! Not all of your peers approach the job in the same way (no offense to anyone!). I've been making tools for 20 years, including micron gauges, and I've seen some of the things that can go wrong. I try to address these issues with each new product. Micron gauges are easily contaminated with oil, and most will just hum happily along without telling you there is a problem (and that the readings you are getting are inaccurate). Over-pressure events do occur...why should you have to send back a gauge for repair in that case? Since the vacuum sensor itself is exposed to ambient gas and it is operated at a high temperature, it can be expected to change over time. Why should you have to keep a second gauge on hand to confirm this, or have to send your gauge back to the factory for recalibration?


    Quote Originally Posted by Tech Rob View Post
    If I hook up the micron gauge and it says 2000 microns, I'm going to do one of three things... That is 1) change the pump oil, 2) go get another cup of coffee, 3) pressurize the system and look for a leak. It's not like I'm going to sit there looking at the leak rate indicator going "Hmm, well, even though it's at 2000 microns, the bluvac says the leak rate is 0... I guess we can go ahead and charge it!"
    At least with the BluVac you can have confidence that the readings you are getting are accurate, and that any problems are not the result of a faulty gauge!


    Quote Originally Posted by Tech Rob View Post
    No disrespect intended... Obviously you're doing something right if you've got half of this site brainwa... I mean using your gauge.
    No offense taken! Believe it or not, I often get better feedback from skeptics than I do from the choir (though I do greatly appreciate my choir! ). I appreciate your comments more than you could know!

    Quote Originally Posted by Tech Rob View Post
    I also want to add that I think it's very cool for you to get on this forum and interact with the folks using your tools, answering questions, and offering instantaneous support. That is very rare and quite invaluable these days!
    I have found that interaction here is very much a two-way street. I learn things that I wouldn't have otherwise discovered myself, and can use that to help me develop better products in the future. At the same time, I can help you all to get the most out of the existing products I offer. Thank you for your participation!

  7. #33
    Join Date
    Mar 2007
    Posts
    3,136
    You're welcome! Thanks for the well-thought out reponse! Does either one of the Bluvac gauges come with a case? A case with a nice little foam insert would be great. This is one of the things that REALLY burns my @$$ about other high-end instrument manufacturers... They don't offer most of their meters and instruments with cases, and if you want to buy one separately, bend over and grab your ankles!
    The key to happiness is lower expectations.

  8. #34
    Join Date
    Nov 2006
    Location
    Athens, Ohio
    Posts
    2,072
    Quote Originally Posted by Tech Rob View Post
    You're welcome! Thanks for the well-thought out reponse! Does either one of the Bluvac gauges come with a case? A case with a nice little foam insert would be great. This is one of the things that REALLY burns my @$$ about other high-end instrument manufacturers... They don't offer most of their meters and instruments with cases, and if you want to buy one separately, bend over and grab your ankles!
    I keep my Bluvac in a compartment of my Appion Megaflow case. It also has a space where I keep my Nylog. I don't mess around when it comes to pulling a vacuum.

  9. #35
    Join Date
    May 2004
    Posts
    1,886
    Joeyd, do they both have the same screen resolution? What is the warranty?

  10. #36
    Join Date
    Aug 2010
    Location
    Florida
    Posts
    251
    Quote Originally Posted by Tech Rob View Post
    You're welcome! Thanks for the well-thought out reponse! Does either one of the Bluvac gauges come with a case? A case with a nice little foam insert would be great. This is one of the things that REALLY burns my @$$ about other high-end instrument manufacturers... They don't offer most of their meters and instruments with cases, and if you want to buy one separately, bend over and grab your ankles!
    We've had such requests already.

    Currently, there is no case/pouch for the BluVac. We are working on a number of accessories for the BluVac/LTE, in addition to creating an evacuation "kit". I don't have any details or release dates at this time, but I will let you know when the info is available.

  11. #37
    Join Date
    Aug 2010
    Location
    Florida
    Posts
    251
    Quote Originally Posted by 270wsm View Post
    Joeyd, do they both have the same screen resolution? What is the warranty?
    If by "screen resolution" you mean the resolution of the micron reading: no, the BluVac has 0.1 micron resolution from 0 to 9,999.9 microns, and 1 micron resolution from 10,000 microns to 25,000 microns. The LTE is 1 micron resolution from 0 to 25,000 microns.

    If you mean the 'physical' characteristics of the actual display, they both use the same blue-backlit LCD display.

    Full details are available at:

    http://accutools.com/index.php?page=...subpage=bluvac

    and

    http://accutools.com/index.php?page=...page=bluvacLTE

  12. #38
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    25,924
    Quote Originally Posted by Tech Rob View Post
    You're welcome! Thanks for the well-thought out reponse! Does either one of the Bluvac gauges come with a case? A case with a nice little foam insert would be great. This is one of the things that REALLY burns my @$$ about other high-end instrument manufacturers... They don't offer most of their meters and instruments with cases, and if you want to buy one separately, bend over and grab your ankles!
    I can see the BluVac sitting very nicely in a small Pelican case.

    http://www.bhphotovideo.com/bnh/cont...=REG&A=details

    Not exactly sure it would be that one in particular, but one very similar to it.

  13. #39
    Join Date
    Apr 2012
    Location
    Milwaukee
    Posts
    28
    Joeyd... pardon my ignorance (as I have only been a registered user for about a 10 days now) but I don't quite understand your relationship with the BluVac. Do you (with your own two hands) actually manuacture the BluVac gauge or is this an instrument of your own engineering and design? I have this picture in my mind of you running service calls all day long, only to go home and sit at your garage/basement workbench, assembling micron gauges, one at a time, component by component all by hand, like a fine Swiss watch maker. Please correct me if I am painting an inaccurate picture. I have NEVER seen a BluVac micron gauge at any of the local refrigeration supply houses in the Milwaukee/Madison area. Additionally, I have never even heard a fellow technician mention the BluVac uge during our ocassional discussions about tools/equipment that every guy should get. I have also asked the Journeyman who teach night school at the union hall and my fellow 4th and 5th year apprentices if they have had any experiences with, or heard anything about the BluVac, but nobody is familiar with the gauge but all of us (apprentices and Journeymen both) are very interested in seeing one in action. I see from some of the previous posts, guys haven't been shy about asking for a sample, but I am wondering if it is possible to obtain a BluVac micron gauge so that I can take the gauge to the hall and show fellow classmates and my teachers how the gauge stacks up against the other products on the market. I could also take it to my work and introduce it to service guys to get their thoughts on it. I work for Advantage Refrigeration, the largest commercial refrigeration/supermarket install and service company in Wisconsin. We always have techs asking for quality vacuum gauges but are purchasing department never knows which to buy. So if I can give tell them that the BluVac gauge is the best on the market on, then we would purchase large quantities for all of service techs

Page 3 of 6 FirstFirst 123456 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event