Thread: PCG MSC for DX cooling
-
04-11-2012, 10:27 AM #1
Professional Member
- Join Date
- May 2011
- Location
- North Carolina
- Posts
- 178
PCG MSC for DX cooling
I have an RTU that I'm using the ODA to reset the DA setpoint. The rtu is suppling air to 13 VAV's with SCR heat. The problem I am running into is the DA temp is going way below the setpoint. I have seen the setpoint be at 55 and the discharge air be at 48. I think it is the MSC that is doing this. I have set the minimum run time to 60 seconds but it seems it keeps going below setpoint. Is there any settings I can change in the multi state controller?
-
04-11-2012, 12:23 PM #2
Professional Member
- Join Date
- Oct 2009
- Posts
- 485
The problem is that you're trying to control dx cooling from discharge air temperature. Have you considered trying to control it from return air temperature?
-
04-11-2012, 06:33 PM #3
Professional Member
- Join Date
- May 2004
- Location
- SE Pennsylvania
- Posts
- 508
How many stages?
-
04-12-2012, 04:24 PM #4
Professional Member
- Join Date
- May 2011
- Location
- North Carolina
- Posts
- 178
There are 2 stages of DX cooling. Igotworms I thought it was going to be a little difficult. I considered doing it to return air but the engineer spec'd DA? That's why I thought resetting the DA would make it a little better. They always complain they are cold since occuping the space about 3 weeks ago.
-
04-13-2012, 10:37 PM #5
Professional Member
- Join Date
- Oct 2009
- Posts
- 485
If the engineer spec'd discharge air then there isn't much you can do. I would just play around with cooling min on/off times.