    PCG MSC for DX cooling

    I have an RTU that I'm using the ODA to reset the DA setpoint. The rtu is suppling air to 13 VAV's with SCR heat. The problem I am running into is the DA temp is going way below the setpoint. I have seen the setpoint be at 55 and the discharge air be at 48. I think it is the MSC that is doing this. I have set the minimum run time to 60 seconds but it seems it keeps going below setpoint. Is there any settings I can change in the multi state controller?

  2. #2
    Join Date
    Oct 2009
    Posts
    485
    The problem is that you're trying to control dx cooling from discharge air temperature. Have you considered trying to control it from return air temperature?

  3. #3
    Join Date
    May 2004
    Location
    SE Pennsylvania
    Posts
    508
    How many stages?

  4. #4
    Join Date
    May 2011
    Location
    North Carolina
    Posts
    178
    There are 2 stages of DX cooling. Igotworms I thought it was going to be a little difficult. I considered doing it to return air but the engineer spec'd DA? That's why I thought resetting the DA would make it a little better. They always complain they are cold since occuping the space about 3 weeks ago.

  5. #5
    Join Date
    Oct 2009
    Posts
    485
    If the engineer spec'd discharge air then there isn't much you can do. I would just play around with cooling min on/off times.