    Do econos work well in church setting because of the larrge heat load at once? The system I am working on consists of 2 large air handlers 2 condensers. The system has economiser installed but all the controls are unhooked. Honeywell econo enthalpy sensor 2 to 10 actuator and Honeywell logic. Just curious if it will be benificial to try and get up and running or leave as is. Also church is in the country very dusty conditions orchards dirt. Any info or insight is appreciated.
    SE Michigan
    I dont see why not....there there to provide a great option to mechanical cooling. If ambient temps are good for cooling, why not use them. Just make sure they are set up properly.
    Not sure why the economizer option was even chosen and paid for if their not being used.
    Would save them on electric bills too.
    “Socialism is a philosophy of failure, the creed of ignorance, and the gospel of envy, its inherent virtue is the equal sharing of misery.”
    Southeastern Pa
    If there is cool dry air available, then hook it all up and test it.
    My gut tells me that the last guy didn't understand the econs, and that's why they are disabled.
    2 Tim 3:16-17
    Member, IAEI
    AOP Forum Rules:
    many guys don't understand the importance of economizers & their function. then there are some who don't care & just bypass it
    Cal
    That's the big question with economizers, do the save more then they cost to maintain? Look up the economizer hours for your area and see how that fits their irregular/inconsistent occupied hours.
    Make the recommendation and let them decide if they want broken down systems.
    NE Alabama
    Don't think of it as a church; think of it in load and what kind of load and the variableness of the load. Is it jut Wednesday and Sunday or is it used for other functions and when and how long/how many. The system doesn't know it's a church, and depending on your local weather the economizer can be a great energy saver. As to why the economizer was installed look at it from the architect or engineer's point of view IE. it makes you look smart and costs more money and you are charging a percentage of cost as your fee.
    Feb 2011
    Chesterfield, Virginia, USA
    Just be careful of your changeover setting. Also consider a mixed air thermostat to stage on the cooling if the outside ambient can't keep up with the load.
    SE Michigan
    Quote Originally Posted by Failure2Comply View Post
    Shouldn't there all ready be one in the blower section?
    Southeastern Pa
    Quote Originally Posted by btuhack View Post
    It is always cheaper to run a fan than it is to run a fan and a compressor or two, plus a couple of condenser fans.
    Maintenance cost on an economizer is negligible. If the logic module fails, its cost is less than a tenth of the compressor when it fails.
    It's not even a competition.
    2 Tim 3:16-17
    Member, IAEI
    AOP Forum Rules:
    Jun 2009
    The only thing I'm worried about getting it running is when its cool enough to economise and the load all comes in at once the second stage will call which I believe is first stage when in econo mode is running and 2nd stage comp will be off when in a church that could or would likely happen . I will try and get model numbers of econo parts.
    Southeastern Pa
    Quote Originally Posted by pillclinton209 View Post
    I don't think there is a reason for concern for the sequence of operation, because if you are using a typical Honeywell logic module, you can adjust the enthalpy setpoint based on four plotted curves, A, B, C, or D.
    Nothing wrong with that.
    2 Tim 3:16-17
    Member, IAEI
    AOP Forum Rules:
    Southeastern Pa
    Can you provide:
    The brand, model and serial number for both units
    The logic module (honeywell) number such as W7459, W7212
    the actuator motor number used in the units
    the stats used to control the units
    Thx
    2 Tim 3:16-17
    Member, IAEI
    AOP Forum Rules:
    Cal
    Quote Originally Posted by timebuilder View Post
    I was thinking more about how many economizer hours ( no mech'l cooling) would have occur during the church schedule to offset a $400.00 repair.
    Comparing compressor repairs to Econ repairs IS a no brainier but a different kettle of fish when the OSA is above 75.... One matters while the other is meaningless.