04-12-2012, 08:15 PM #28
You might not be able to use filter racks in the conditioned area because you have too many ducted return grilles, etc.
For a 3-Ton system you could use two drops, one to each side of the furnace Return chamber.
Hart&Cooley Engineering Data, a 24X20 media type filter provides 2.3-sf (Ak) of free-air-area & will flow 713-CFM of air at 300-fpm velocity through it.
Therefore, it takes two of those filters @300-fpm to get above 1350-CFM, or 1426-CFM a little extra area is always better as filters load...
If you only used one of those filters at 1200-CFM / 2.3-sf (Ak) is 522-fpm Velocity through the filter; above 500-fpm debris blows through a fiber glass filter.
As a media filter loads the free-area becomes less & the velocity will soon reach 500-fpm limit with the low cost filters.
A one inch thick pleaded filter will have too much pressure ]drop & loads only on the surface area of the filter.Last edited by udarrell; 04-12-2012 at 08:36 PM. Reason: 1426-CFM a little extra area is always better as filter load...
AOP Forum Rules:
Rules for Posting
Rules For Equipment Owners
Equipment Owners Find a Contractor HERE!
udarrell
-
04-12-2012, 08:22 PM #29
Then the office will have a higher R value insulation in its walls then the bedroom does, so it will lose and gain less heat then the bedroom does. Roughly 30% less heat loss and gain. Where the office adjoins to the bedroom, will eliminate the heat loss and gain that bedroom wall use to have.
The choices you make today, will be the electric bills you have to pay later.
-
04-13-2012, 11:00 AM #30
Regular Guest
- Join Date
- Apr 2012
- Posts
- 26
-
04-13-2012, 11:03 AM #31
Regular Guest
- Join Date
- Apr 2012
- Posts
- 26
-
04-13-2012, 12:49 PM #32
It does not increase the flow per minute, it divides the amount of air in half passing through the same open-area of the filters & thus reduces the fpm velocity.
You're not adding the filter in one single Return Air stream for the entire home, you're splitting the Return Air in half by dividing the required amount of air flow between two return filters that enter the two sides of the furnace. This larger free-air-area also reduces air resistance & the total pressure drop of the RA filtering system.
The furnace normally has two knock-out areas on both (Right & Left) sides & the bottom so that RA can enter the furnace return chamber from three differing area sources...
If you were to use two filter-racks in the conditioned areas then you would never use a filter in the furnace as that would be two filters doubling filtering one air stream which would greatly increase the pressure drop resistance.
If you were using only 16X25 filter grilles @1.7625-sf of open-area flowing 680-CFM @300-fpm velocity = 1269-CFM, it would take two of them in different areas of the home to achieve over 1200-CFM of air flow @300-fpm velocity through those two filters.
Many 3-Ton furnaces will have knock-outs that will only receive a maximum of a 16X25 duct.
Therefore many will only have one entry to the furnace return air chamber using one 16X25 filter; @1200-CFM / 1.7625-sf open-air-area is 680-feet per minute (fpm) velocity through that new clean filter. Well, there would be NO filter grille restrictions so it wouldn't be quite that high a velocity.
However, it would need two entries with a filter in each, to efficiently flow 1200-CFM for a 3-Ton system at an initial 300p-fpm or less velocity through the filters.
This is an important area to gain system efficiency of air flow that is rarely done by the book; but we should try to achieve it whenever possible. IMO, It ought to be part of the code...
The 18X28 results in around 540-fpm velocity through a clean filter; if you're using a 4 or 5-inch thick pleated filter you can start at 500-fpm velocity through it.Last edited by udarrell; 04-13-2012 at 12:56 PM. Reason: 18X28 filter...
AOP Forum Rules:
Rules for Posting
Rules For Equipment Owners
Equipment Owners Find a Contractor HERE!
udarrell
-
04-13-2012, 04:45 PM #33
-
04-16-2012, 08:19 PM #34
Regular Guest
- Join Date
- Apr 2012
- Posts
- 26
A great explanation. So can you confirm for me the needed CFM using the specs I posted earlier for the potential system that will be used. I'm uncertain how you derive the minimum needed flow unless this is a standard spec for all 3 Ton units. Further more, I take it most installers won't split the return and rather will just use a single knock out. In fact, it's my understanding that the HVAC contractor has to add the filter shelf as the furnance doesn't come with it by standard. Lastly, my current filter is a washable sponge type material. It's no where near 5 inches thick but I would think it flows well.
-
04-16-2012, 08:28 PM #35
Regular Guest
- Join Date
- Apr 2012
- Posts
- 26
-
04-16-2012, 08:42 PM #36
-
04-17-2012, 07:09 AM #37
Regular Guest
- Join Date
- Apr 2012
- Posts
- 26
-
04-17-2012, 09:30 AM #38
If the system is zoned it might be a disadvantage to go from 2.5-Ton to a 3-Ton system which requires more airflow to handle per zone.
The 3.5" X 13" is around 0.316-sf duct area which is close to a 7.5" rd duct at around 0.307-sf area.Well, the current supplies are 3.5" x 13" in size so what would those provide?
According to my airflow software; the 7.5" duct flowing 140-CFM on a long 50' run with (2) 90's, velocity is only 457-fpm, friction rate is 0.04" over the 50 foot run; or 0.06" FR per 100 foot.
Run a Return air duct at least that large back to the air handler & with a zoned system the 1st floor & 2nd floor zone thermostat will allow you to control to any temp you want within each zone.
With programmable thermostats on each zoned level you can save on your utility bills by programming the cooling & heating according to which zoned level you'll be on during specific hours of the day or night.
There are some real advantages with a properly zoned system.Last edited by udarrell; 04-17-2012 at 09:41 AM. Reason: Removed some content...
AOP Forum Rules:
Rules for Posting
Rules For Equipment Owners
Equipment Owners Find a Contractor HERE!
udarrell
-
04-17-2012, 09:34 AM #39
An accidental double post!
Last edited by udarrell; 04-17-2012 at 09:38 AM. Reason: BEENTHERE; Didn't think the first post worked; double post REMOVE THIS ONE
AOP Forum Rules:
Rules for Posting
Rules For Equipment Owners
Equipment Owners Find a Contractor HERE!
udarrell


Reply With Quote

I'm not the HVAC contractor though so my logic may be off.