    May 2009
    Waterloo Ontario
    Higher ton evap coil, with lower ton cond
    hey guys,
    I've been told that when matching up a cond and evap, if you use a larger evap coil it will increase the seer rating?
    Ive got a 2 ton lennox heat pump, and a 3 ton case coil made by lennox as well.
    How does this effect the seet rating? is it stickly because of the increased size of the evap surface area?
    The saturated temperature/pressure will be higher with a larger evaporator coil, which lowers the compression ratio, so the compressor uses less energy for a similar amount of cooling.
    The total btuh capacity typically goes up slightly, but so does the sensible heat ratio, so humidity control can suffer a bit.
    Madison, WI/Cape Coral, FL
    Add- " so humidity control can suffer a bit" unless the air is flow is slowed enough to lower the coil temperature several degrees below the desired inside dew point. Slowing the air flow will remove more moisture while maintaining a higher suction capacity. The negative factor is that more moisture is needed to get the coil to drip to the drain and retained on the larger coil which will evaporate into the home at the end the cooling cycle. This affects the muli-speed a/cs in a big way. They lower cooling capacity will very large coils. 1-2 lbs. moisdture per ton are need on a coil to start draining. At the end of the cycle, the retained moisture evaporates back into the home. Make the cooling cycle are long as possible. Using a whole house dehumidifier for maintaining <50%RH during low/no cooling loads is much more effective.
    Regards TB