    Is New Compressor Needed?

    Symptom: Had an 80* OAT day and turned on AC. 83* inside. Inside set at 77*. While vent air seemed reasonably cool, took 1-3 hours to drop to 80* inside. Hours later, dropped to 79* inside.

    Current HVAC:

    Gas Furnace: 92.2 AFUE York/Unitary P3URC14N09501D
    Coil: York/Unitary G1UA036S21C R22 or R410A option but don't know which is being used
    Compressor: Goodman CKJ30-1A

    Don't know furnace/coil age but booklets for furnace/coil are copyright 1999-2000. Service guy says compressor is from 2000, but I did not see on label (I wasn't present for service call).

    Service guy told wife 2-ton compressor worn out from age. $$$$ to replace but no specifics on brand/model.

    Question-do I need a new compressor? If so, do I replace compressor or start with a new system from scratch (say a heat pump). Thank you for any help.
    Last edited by jpsmith1cm; 04-10-2012 at 09:57 PM. Reason: Pricing

  2. #2
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    I'd be looking for a second opinion.

    a. If it's cooling at all, the compressor is probably fine.

    b. A 12 year old compressor isn't "worn out from age"



  3. #3
    Join Date
    Aug 2004
    Location
    North Richland Hills, Texas
    Posts
    15,732
    Post Likes
    Quote Originally Posted by jpsmith1cm View Post
    b. A 12 year old compressor isn't "worn out from age"
    This!

    If a 12 year old compressor is dead, it wasn't old age, it was murder.

  4. #4
    Join Date
    May 2005
    Location
    midwest USA
    Posts
    95
    Post Likes
    Thread Starter
    Today, I talked with the service guy. He said the low pressure is 52 and the high is 68, indicating bad valves and necessitating replacement of the compressor. Although he charged me for a full routine AC service, he said he never looked at the inside unit other than to check the filter.

    He had also suggested to my wife yesterday that replacing the whole sytem makes more sense than just replacing the compressor. I'm not sure how he came up with that recommendation if he didn't look at inside system (furnace/fan/coil).

  5. #5
    Join Date
    May 2008
    Location
    Missouri
    Posts
    4,384
    Post Likes
    This is a 2 1/2 ton unmatched system. At 12 years of age, I'd not recommend replacing the compressor. Replace the entire system with a matched system (inside and outside units).

  6. #6
    Join Date
    Jun 2005
    Location
    SW Wisconsin
    Posts
    6,627
    Post Likes
    Quote Originally Posted by scouts22 View Post
    Symptom: Had an 80* OAT day and turned on AC. 83* inside. Inside set at 77*. While vent air seemed reasonably cool, took 1-3 hours to drop to 80* inside. Hours later, dropped to 79* inside.

    Current HVAC:

    Gas Furnace: 92.2 AFUE York/Unitary P3URC14N09501D
    Coil: York/Unitary G1UA036S21C R22 or R410A option but don't know which is being used
    Compressor: Goodman CKJ30-1A [12-SEER 2.5-ton +1998-2000, think it's R-22]

    Don't know furnace/coil age but booklets for furnace/coil are copyright 1999-2000. Service guy says compressor is from 2000, but I did not see on label (I wasn't present for service call).

    Service guy told wife 2-ton compressor worn out from age. $$$$ to replace but no specifics on brand/model.

    Question-do I need a new compressor? If so, do I replace compressor or start with a new system from scratch (say a heat pump). Thank you for any help.
    scouts22;Today, I talked with the service guy. He said the low pressure is 52 and the high is 68, indicating bad valves and necessitating replacement of the compressor. Although he charged me for a full routine AC service, he said he never looked at the inside unit other than to check the filter.

    He had also suggested to my wife yesterday that replacing the whole system makes more sense than just replacing the compressor. I'm not sure how he came up with that recommendation if he didn't look at inside system (furnace/fan/coil).
    With bad valves normally the low side is not a low 52-psig pressure, but a high low side pressure; with bad compressor valves the high-side head pressure drops & the suction pressure rises way above normal. That reported scenario sounds fishy to me...may just be wanting an equipment change-out...?

    Small chance, but perhaps the valve core was not depressed enough to get an accurate high-side reading; but I question what took place by the service guy.

    If the pressures were as he indicated there would be no cooling. What is the temperature of the air coming off the condenser as compared to the outdoor temp; list both temps.

    What is the temps of supply air & return air in your home?
    There are other indications that don't make sense with what you were told...

    There are other diagnostic checks that a PRO could use. A blocked filter-drier inside the condenser could cause a very low high-side reading at the liquid high-side port as the liquid refrigerant merely builds up in the condenser; a condenser can hold all of the liquid refrigerant in the system.

    By all means find another contractor for a more comprehensive diagnosis & opinion; don't tell them what the other guy said.
    Last edited by udarrell; 04-11-2012 at 12:11 PM. Reason: think it's R-22...

  7. #7
    Join Date
    May 2005
    Location
    midwest USA
    Posts
    95
    Post Likes
    Thread Starter
    udarrell: "If the pressures were as he indicated there would be no cooling."

    jpsmith1cm: "If it's cooling at all, the compressor is probably fine."

    The service guy did mention when I called him today that he was "surprised" I was getting some cooling. Guess that means he realizes there may be a flaw in his diagnosis but he didn't follow up on it.

    BTW, I can't figure out how to make the multi-quote thing work here. I'm maxed out at one quote. Thanks.

  8. #8
    Join Date
    Jun 2005
    Location
    SW Wisconsin
    Posts
    6,627
    Post Likes
    Quote Originally Posted by scouts22 View Post
    udarrell: "If the pressures were as he indicated there would be no cooling."

    jpsmith1cm: "If it's cooling at all, the compressor is probably fine."

    The service guy did mention when I called him today that he was "surprised" I was getting some cooling. Guess that means he realizes there may be a flaw in his diagnosis but he didn't follow up on it.

    BTW, I can't figure out how to make the multi-quote thing work here. I'm maxed out at one quote. Thanks.
    Well, there could be some cooling with a partially plugged liquid line filter-drier inside the condenser; depends on the extent it's plugged.

    Depending on outdoor dew point, frost should be indicated on filter-drier & down-stream from it, if no frost due to very low dew point temp,the drier & down-stream tubing should be a lot colder than up-stream toward condenser coil.

    The pressures indicate is NOT bad valves.

    A clogged liquid line filter-drier inside the condenser is the most likely cause of a pull-down on the liquid line pressure port; it would turn the liquid line into a virtual suction line pull down condition.

    If the liquid line service valve were nearly closed by someone servicing the system the same condition would occur.(?)

    Let's hope that didn't happen...

    Sorry to be so negatively speculative... but the signals are there...
    -----
    Hi-lite the other post you want to quote & paste it below the original Quote, then hi-lite it again & click on the Quote tab, 4th from the right, - that will also Quote it.

  9. #9
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    Quote Originally Posted by scouts22 View Post
    Today, I talked with the service guy. He said the low pressure is 52 and the high is 68, indicating bad valves and necessitating replacement of the compressor. Although he charged me for a full routine AC service, he said he never looked at the inside unit other than to check the filter.

    He had also suggested to my wife yesterday that replacing the whole sytem makes more sense than just replacing the compressor. I'm not sure how he came up with that recommendation if he didn't look at inside system (furnace/fan/coil).
    I do not accept this diagnosis.

    I would expect MUCH different pressures from a failed compressor.

    If you've got the cash, a new system is a good way to go, but I'll bet that this one can be repaired for less money.

    Have a look at our Contractor Locator Map and see if there is a contractor near you.



  10. #10
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    Quote Originally Posted by scouts22 View Post
    udarrell: "If the pressures were as he indicated there would be no cooling."

    jpsmith1cm: "If it's cooling at all, the compressor is probably fine."

    The service guy did mention when I called him today that he was "surprised" I was getting some cooling. Guess that means he realizes there may be a flaw in his diagnosis but he didn't follow up on it.

    BTW, I can't figure out how to make the multi-quote thing work here. I'm maxed out at one quote. Thanks.
    This scares me a little.

    IF you don't have faith in your tech, then you need to replace him, not a compressor that is still doing it's job.



  11. #11
    Join Date
    Dec 2002
    Location
    Houston,Texas
    Posts
    23,010
    Post Likes
    Quote Originally Posted by jpsmith1cm View Post
    I do not accept this diagnosis.
    I would expect MUCH different pressures from a failed compressor.
    Those pressures don't indicate any bad valves to me, something is wrong if it has those pressures, but bad valves?
    __________________________________________________ _______________________
    “Experience is a hard teacher because she gives the test first, the lesson afterwards" ~ Vernon Law

    "It's what you learn after you know it all that counts." ~ John Wooden

    "When the teachers become unteachable we're all in trouble" ~ Mr. Bill

    "Remember "Pro" is only a name, it's not always a mindset determined to do everything correctly" ~ Mr. Bill




  12. #12
    Join Date
    Jun 2005
    Location
    SW Wisconsin
    Posts
    6,627
    Post Likes
    Depending on outdoor dew point, frost should be indicated on filter-drier & down-stream from it, if no frost due to very low dew point temp,the drier & down-stream tubing should be a lot colder than up-stream toward condenser coil. [That was an incorrect statement by me!]
    My quoted post above needs some clarification.

    Dew point is relevant to when a suction line sweats or not.
    It's not relevant to when a line gets below the freezing point.

    Let' take an R-22 TXV metered evaporator set for 12-F superheat.

    First load is very light & you read only 62-psig suction that's only 35-F Saturated Suction Temp (SST), add 12-F Superheat & the line temp is 47-F, usually the dew point is going to be well above that temp. That is even above beer-can cold.

    Second load is an 85-psig with a 51-SST add 12-F SH 63-SLT.
    The dew point could be below that temp & therefore NO sweating on the line; also a 63-F suction line is not going to feel beer-can cold.

    We have to take both the suction & high-side refrigerant line temps & pressures & do the math to get both Superheat & Subcooling so we know what we're doing; beer-can cold & a sweating line does not work, it's even more critically important on high SEER systems that operate at higher suction pressures & line temps, with a given heatload....
    Last edited by udarrell; 04-12-2012 at 09:20 AM. Reason: [That quote was an incorrect statement by me!]

  13. #13
    Join Date
    May 2008
    Location
    Central Fla.
    Posts
    311
    Post Likes
    Sounds like you need a more qualified tech to check this out.

  14. #14
    Join Date
    May 2005
    Location
    midwest USA
    Posts
    95
    Post Likes
    Thread Starter
    Delete

  15. #15
    Join Date
    May 2005
    Location
    midwest USA
    Posts
    95
    Post Likes
    Thread Starter
    Quote Originally Posted by udarrell View Post
    My quoted post above needs some clarification.

    Dew point is relevant to when a suction line sweats or not.
    It's not relevant to when a line gets below the freezing point.

    Let' take an R-22 TXV metered evaporator set for 12-F superheat.

    First load is very light & you read only 62-psig suction that's only 35-F Saturated Suction Temp (SST), add 12-F Superheat & the line temp is 47-F, usually the dew point is going to be well above that temp. That is even above beer-can cold.

    Second load is an 85-psig with a 51-SST add 12-F SH 63-SLT.
    The dew point could be below that temp & therefore NO sweating on the line; also a 63-F suction line is not going to feel beer-can cold.

    We have to take both the suction & high-side refrigerant line temps & pressures & do the math to get both Superheat & Subcooling so we know what we're doing; beer-can cold & a sweating line does not work, it's even more critically important on high SEER systems that operate at higher suction pressures & line temps, with a given heatload....
    I presume your comments are directed at your fellow techs as they're over my head. Nonetheless, they raise another question. Is there a minimum OAT to troubleshoot this or other issues?

    Thanks to everybody that replied. This is one of the best forums on any subject anywhere.

    I wish I could retain one of you experts for my HVAC needs. I looked at the contractor locator map but there is only one listing in the Kansas City area, but that contractor only has a Facebook page with no info about the company other than a phone number. He may be great, but the lack of info about the company doesn't inspire confidence. Not sure how I could search for postings on this forum by the contractor. I searched the company name, but no luck.

  16. #16
    Join Date
    May 2005
    Location
    midwest USA
    Posts
    95
    Post Likes
    Thread Starter
    Delete

  17. #17
    Join Date
    May 2005
    Location
    midwest USA
    Posts
    95
    Post Likes
    Thread Starter
    Had my second opinion. They put in 3 lbs of R-22. Everything else was fine. I moved in two years ago, so not sure when last service was to gauge rate of refrigerant loss. Guess we'll see next year.

  18. #18
    Join Date
    Jun 2005
    Location
    SW Wisconsin
    Posts
    6,627
    Post Likes
    Quote Originally Posted by scouts22 View Post
    Had my second opinion. They put in 3 lbs of R-22. Everything else was fine. I moved in two years ago, so not sure when last service was to gauge rate of refrigerant loss. Guess we'll see next year.
    You may not have to wait until next year to find out...

    So, they didn't locate the leak & fix it.
    The least they could do is locate the leak; if it's a large enough leak it should be easy to find.

    Also needs to indicate whether the leak is on the high-side or low-side; low-side leaks can mean a lot of air & moisture drawn into the system.

    Refrigerant is expensive...over-time moisture in the system is also very costly...

  19. #19
    Join Date
    May 2005
    Location
    midwest USA
    Posts
    95
    Post Likes
    Thread Starter
    Quote Originally Posted by udarrell View Post
    You may not have to wait until next year to find out...

    So, they didn't locate the leak & fix it.
    The least they could do is locate the leak; if it's a large enough leak it should be easy to find.

    Also needs to indicate whether the leak is on the high-side or low-side; low-side leaks can mean a lot of air & moisture drawn into the system.

    Refrigerant is expensive...over-time moisture in the system is also very costly...
    They didn't say about hi/lo. Yes, putting in that much refrigerant is not something I would do more than once. They indicated that locating a leak is generally too difficult and did not attempt. What is involved with locating a leak? Thank you.

  20. #20
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,690
    Post Likes
    Quote Originally Posted by scouts22

    They didn't say about hi/lo. Yes, putting in that much refrigerant is not something I would do more than once. They indicated that locating a leak is generally too difficult and did not attempt. What is involved with locating a leak? Thank you.
    Sounds like a lazy tech.

    My experience is that a quality leak detector and a skilled tech can find leaks fast



Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •