    I'm working on a 3 ton Trane ac system....bout 12 yrs old...
    The house is not cooling properly.
    83 degree outdoor
    Low side 74 psi, 1.9 super heat.
    Hi side 178 Psi, 3 subcool
    18 temp drop across the coil... 81 return - 63 supply.
    I couldn't figure out what's wrong with it
    Sep 2006
    you want to check the square feet of the house it's look like you compressor is a week your low side should be about 60 65 PSI
    make sure your square feet is the same as the regional NO extension added also I'm not sure where the system if it's an attic make sure you don't have any doubt leaks including the return
    http://www.liebertairconditioning.com
    Wet bulb temps would help.
    As would airflow.
    I do not suspect your compressor, but I do suspect multiple problems here.
    Low airflow and low charge most likely.
    Feb 2012
    Quote Originally Posted by DNMechanical View Post
    83 degree outdoor
    1.9 is a bit low for super heat.
    Does the unit have a TXV or fixed orifice?
    What type of refrigerant is in the unit?
    I'm thinking it's overcharged but we need more information on the unit.
    Mar 2012
    Grand Prairie, TX
    r-22. fix orifice. I pretty sure it had multiple problems but just couldn't figure it out ..unit is in attic.. no no air leak....
    Quote Originally Posted by AStudent
    Subcooling indicates a low charge.
    Low superheat tends to point towards a low airflow, particularly since the subcooling is low as well.
    Feb 2012
    High side pressure too high...low side is spot on..with a fixed orifice. What does this indicate?
    Not thinking about an air leak, I'm thinking that you don't have enough air moving across the evaporator coil.
    Mar 2012
    Grand Prairie, TX
    if not enough air move across evap, it will cost low suction presure
    Mar 2012
    Grand Prairie, TX
    @ASTUDENT.... high side is too low (NOT HIGH). low side is about right...
    Pressures alone are largely meaningless.
    It will cause low Superheat, first,
    Your 81 degree return temp would help to keep that suction pressure up.
    Did you measure the airflow?
    Low high side pressure would be consistent with low load caused by low airflow.