coil stats ?
working on turbo air reach in cooler. unit had two issues, one was a leak which i fixed.. While testing the unit, i found it would pull down to around 25 degrees and wouldn't satisfy..
so i put a new stat on it, i dont like coil stats and would much rather have a air stat, but i doos as i told, it was a ranco a21 i think, but dont quote me on that, it was still doing the same thing.
i had to get out of there as it was getting really busy, last temp i had was 26 and still running.They told me to use the brain God gave me.
I did.
Now I'm an Atheist. Ironic, isn't it?
-
04-07-2012, 09:16 AM #2
Professional Member
- Join Date
- Dec 2003
- Location
- chicago,il
- Posts
- 97
i use a ranco a12-1560 used them for years no problems
-
04-07-2012, 11:20 AM #3
Professional Member
- Join Date
- Mar 2006
- Posts
- 955
-
04-07-2012, 12:32 PM #4
Did you have the control's cap tube inserted in the coil properly with the recommended 6" into the coil? What setting did you have the control set at?
The A12-1560 has a mid-range or "normal off" of about 24ºF, which would be around #4 or #5 on the dial. Remember, the higher the number, the colder the cut-out temp.
Here's an old thread on constant cut-in controls:
http://hvac-talk.com/vbb/showthread.php?t=108790