    955

    coil stats ?

    working on turbo air reach in cooler. unit had two issues, one was a leak which i fixed.. While testing the unit, i found it would pull down to around 25 degrees and wouldn't satisfy..

    so i put a new stat on it, i dont like coil stats and would much rather have a air stat, but i doos as i told, it was a ranco a21 i think, but dont quote me on that, it was still doing the same thing.

    i had to get out of there as it was getting really busy, last temp i had was 26 and still running.
    They told me to use the brain God gave me.
    I did.
    Now I'm an Atheist. Ironic, isn't it?

  2. #2
    Join Date
    Dec 2003
    Location
    chicago,il
    Posts
    97
    i use a ranco a12-1560 used them for years no problems

  3. #3
    Join Date
    Mar 2006
    Posts
    955
    Quote Originally Posted by gmfridg View Post
    i use a ranco a12-1560 used them for years no problems
    thats what it was
    They told me to use the brain God gave me.
    I did.
    Now I'm an Atheist. Ironic, isn't it?

  4. #4
    Join Date
    Jul 2000
    Location
    Treasure Coast/Florida
    Posts
    9,793
    Did you have the control's cap tube inserted in the coil properly with the recommended 6" into the coil? What setting did you have the control set at?

    The A12-1560 has a mid-range or "normal off" of about 24ºF, which would be around #4 or #5 on the dial. Remember, the higher the number, the colder the cut-out temp.

    Here's an old thread on constant cut-in controls:

    http://hvac-talk.com/vbb/showthread.php?t=108790