04-07-2012, 12:45 AM #1
Regular Guest
- Join Date
- Dec 2011
- Location
- louisiana
- Posts
- 50
h10G leak detector
Hoping more people in another thread would advise about their favorite electronic leak detectors, but....., am looking at a hardly used Bacharach H10G, Mars 25303 on Ebay. have H10's changed much or is an H10G an H10G , is it worth looking at or if I am going to drop a bundle, should I go for the H10 PM? Was thinking the Ebay H10G would go for a few hundred, but don't know if there are parts that wear out and need replacing or if the newer ones are more efficient. I don't mind paying for something that works, not a brand name.
Thanks
Greg
-
04-07-2012, 07:17 PM #2
Professional Member*
- Join Date
- Oct 2009
- Location
- God's country - Shenandoah Valley, VA
- Posts
- 195
The H10 (with whatever suffix) Is still the best leak detector available. I got a new one last year and it's still the same basic unit with some minor improvements. There's also a battery powered model available.
-
04-08-2012, 12:07 AM #3
H10 G is what I use.
Remember, Air Conditioning begins with AIR.
-
04-08-2012, 06:42 PM #4
I also use the H10G , i love it will never waste my money on anything less! be careful buying them used. there very sensitive and easy to screw up. I went to help one of our guys fine a leak a while back, and he took it apon himself to see if it was working and stuck it straaight in a stream of refigerant. saturated the sensor in it (new sensor $103) thats the last time he will ever look at much less touch my sniffer. If your get one keep it away from careless hands.
-
04-08-2012, 09:39 PM #5BS.
Originally Posted by david912
You won't ruin an H-10 sensor that way.
I've done it enough to know.
-
04-08-2012, 09:57 PM #6
Water is a different story. I've unfortunately done a few doozey's with water and H-10's though, even being very careful. When you realize you've done it, it's too late. Time for a repair.
I always swore by my H-10's, until R-410 came along. Then I began to second-guess them. We have had decent results with the TifZX on 410. It has been a while since I've done 'duelling leak detectors' on 410. Might have to give it a go again.
-
04-08-2012, 10:00 PM #7Ditto on water. Not good for pumps.
Originally Posted by thermojohn
The h-10 works great on HFCS refrigerants. Far better than the Inficon, TIF and CPS models that I've tried.
-
04-11-2012, 05:26 PM #8
Professional Member*
- Join Date
- Mar 2003
- Posts
- 1,215
As others have stated the H10G is by far the best. However be cautious of anything off the internet. Yesterday one of our dealers brought in a "new" H10 he just bought on e-bay and asked me to check it out for him. It was actually a H10 B which was what I used 30+ years ago. It would not sense anything and there are no longer parts to repair the B model. OUCH !
For checking R410 you can adjust the heat range for the sensor by turning the screw located on the back of the case ( without removing it ) full clockwise and then back it back about a 1/4 turn. For the very best results on hard to locate leaks recover the r410 and add a little r22 and nitrogen and then leak check. All detectors are not as sensitive or accurate with R410.
-
04-11-2012, 09:43 PM #9
BS huh! I watched it happen, after the guy Saturated the sensor, i tried to get it around 2 clicks a second and it wouldnt even stay clicking, and it also wouldnt alert on the calibration bottle or r22, tried to calibrate it and didnt help.. put a new sensor and it works like a champ.
-
04-11-2012, 09:48 PM #10
-
04-11-2012, 10:02 PM #11
-
04-11-2012, 11:16 PM #12
Professional Member*
- Join Date
- Oct 2003
- Location
- las vegas
- Posts
- 1,505
-
04-13-2012, 12:15 PM #13
New Guest
- Join Date
- Apr 2012
- Posts
- 1
The sensor will be damaged by a large intake for R134A or R12.
I have been using the H10s for over 20 years, been through 5 units and 12 or more sensors.


Reply With Quote
it up. And it was on a 20 ton york. Anyway its all good man you got it.