testing for non-condensables
Can someone explain this "comparison between the liquid refrigerant pressure and corresponding saturation temperature at ambient conditions " can show if non-condensables or foreign gases are present???
I mean excessive high side pressure does not always mean moisture in system, could be over charge, no fan (ok, some things are obvious), but exactly how can I use these tests to pin down moisture?
Thanks
Greg
-
04-01-2012, 10:34 PM #2
Professional Member*
- Join Date
- Dec 2004
- Location
- Chicago area
- Posts
- 1,386
The test
add a pressure tap to the inside of the condenser, if there is not one already.
Close the refrigeration service valves. Turn on ONLY THE FAN.
let it run for a few minutes. Test the pressure and compare to the corresponding temperature on the gauge. That temperature should match the outdoor ambient.
I am not aware of this test being accurate when the system is running.
This test can also be useful in finding what refrigerant is in the system on refrigeration units.
-
04-02-2012, 12:24 AM #3
Regular Guest
- Join Date
- Dec 2011
- Location
- louisiana
- Posts
- 50
Could you explain the science behind this? I guess I never thought the refrigerant was in a liquid state in the condensor coil when the unit was off. So if moisture is present, corresponding temp would be off(higher?), fan is to ...?
Thanks for your help
Greg
-
04-02-2012, 05:44 AM #4
The fan is to coll the refrigerant to ambient temp. Without the fan running, solar heat could raise the temp and pressure of the refrigerant above the ambient temp.
-
04-02-2012, 07:03 AM #5
see below>>>
Jason J Saylor
Lockheed Martin
HVAC Tech
Meymanah,Afghanistan
"You will encounter many distractions and many temptations to put your goals aside: The security of a job, a wife who wants kids, Whatever. But if you hang in there, always following your vision, I have no doubt you will succeed.”
Larry Flynt quote
-
04-02-2012, 07:04 AM #6
The Science behind it is Every freon has a Temp/Pressure Chart and The pressure is Relative to the ambiant air. For example I can put a pressure gauge on a Can of R22 freon and compare that to a PT chart and tell you the ambiant air temp. Now IF i know the AMbiant temp, and Know the pressure of the Gas and have a chart I can
Jason J Saylor
Lockheed Martin
HVAC Tech
Meymanah,Afghanistan
"You will encounter many distractions and many temptations to put your goals aside: The security of a job, a wife who wants kids, Whatever. But if you hang in there, always following your vision, I have no doubt you will succeed.”
Larry Flynt quote
-
04-02-2012, 11:20 AM #7
Professional Member
- Join Date
- Nov 2011
- Location
- Charleston, Wv.
- Posts
- 677
Dalton's Law....the law of partial pressures, states: that the total pressure of a mixture of gasses is equal to the sum of their individual pressures.
-
04-02-2012, 11:40 AM #8

Pure refrigerant will reflect the pressures on the PT chart. Those pressures are saturation pressures. Yes, it means that liquid can be present, but vapor can also be present at those temperatures. It's called saturation.
Add non-condensible gasses to the container (system) and you will see higher pressures.
-
04-03-2012, 12:22 AM #9
Nice test. Thanks!
-
04-04-2012, 05:05 PM #10
Professional Member*
- Join Date
- Mar 2003
- Posts
- 1,215
-
04-04-2012, 06:01 PM #11
-
07-18-2012, 09:24 PM #12
Professional Member
- Join Date
- Jun 2009
- Location
- Pompano Bch, S Fla
- Posts
- 57
Came across this thread and I don't know what exactly a pressure tap is. Is it a line piercing valve? If so, don't those have a reputation for leaking after a while? Any info would be greatly appreciated. Thanks in advance.
-