Page 1 of 3 123 LastLast
Results 1 to 13 of 31
  1. #1
    Join Date
    Feb 2012
    Location
    Savannah, NY
    Posts
    67

    Federal open face cooler freezing

    Freezing starts at TXV and continues to the evap coil. 404ALow side is 43.2. High side is 323. SH is 20SC is -45. 5.12 amps on run wire from compressor. Do you think I have a restriction in the TXV or am I low on 404?I have evacuated this thing twice and put in 64oz as specs say. It ran fine for about 3 weeks then started freezing up. Any help is greatly appropriated. Thanks

  2. #2
    Join Date
    Mar 2006
    Posts
    947
    id say pull the gas out, replace txv, while its out blow both sides out with nitrogen. make sure your pulling a DEEP vacuum
    They told me to use the brain God gave me.
    I did.
    Now I'm an Atheist. Ironic, isn't it?

  3. #3
    Join Date
    Oct 2008
    Location
    mid-Tennessee
    Posts
    260
    I agree with the TXV. The high discharge pressure is an issue too though. You didn't mention concern over that, but check that condenser and clean it good. POE oil doesn't fare well to a high side running hot.

  4. #4
    Join Date
    Jul 2000
    Location
    Treasure Coast/Florida
    Posts
    9,746
    Post the model number of the case and we'll have a much better chance of helping you.

    Where were you measuring the superheat? At the evaporator outlet or at the compressor? A 20ºF SH might be OK at the compressor but way too high at the evap outlet.

    Did you say 45ºF subcooling? That's too high, but may be explainable if your evaporator SH is high as well...and there's no receiver.

    The Federal cases I've seen are control temperature by a low pressure control, typically set at around 42#CO/85#CI for R404A and defrost is controlled by a mechanical timeclock. I'd start by verifying these items' operation along with proper SH before condemning the TXV.

    Do you have the manual? Here's Federal's manuals page:

    http://www.federalind.com/index.php?...ls-parts-lists

  5. #5
    Join Date
    Feb 2012
    Location
    Savannah, NY
    Posts
    67
    Yes I do have the manual thank you

    Model is SC478

    SC Temp is Negative 45 not positive 45
    Measuring SH next to compressor so yes 20 is not bad. Measuring SC just before the condenser coil.
    I am concerned about the high pressure on the high side sorry I don't mention it.
    Also pressure setting are set to the manual which are 42 & 82. I was thinking maybe the pressure switch was bad because it will come on then the low side pressure will drop fast but not low enough to shut it off according to set pressure but it will shut down.
    Thanks for all the help!!

  6. #6
    Join Date
    Sep 2005
    Location
    florida
    Posts
    5,434
    Quote Originally Posted by mwright View Post
    Yes I do have the manual thank you

    Model is SC478

    SC Temp is Negative 45 not positive 45
    Measuring SH next to compressor so yes 20 is not bad. Measuring SC just before the condenser coil.

    I am concerned about the high pressure on the high side sorry I don't mention it.

    You need to take sh at the evap coil as well.
    I love the smell of phosgene first thing in the morning:

    To apply for professional membership click here


    Educational forums are open.

    If you would like to submit a link or an article or other related info to the EF. click here

  7. #7
    Join Date
    Feb 2012
    Location
    Savannah, NY
    Posts
    67
    Quote Originally Posted by crackertech View Post
    You need to take sh at the evap coil as well.
    So take it next to the TXV? The TXV is a bout 10" from the evap coil.

  8. #8
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    2,736
    Any air diffusers located above the unit? Honeycombs clean?
    Local 597 Service Fitter
    Metal Trade Journeyman

    PAY ME NOW OR PAY ME LATER

    It was working when I left...
    WWFD

  9. #9
    Join Date
    Jul 2000
    Location
    Treasure Coast/Florida
    Posts
    9,746
    For evaporator superheat you need to measure the temperature at the outlet end of the coil where the TXV bulb is attached.

    For subcooling, you need to measure the temperature at the outlet of the condenser coil.

    There is no such thing as negative subcooling. It sounds like you were measuring the discharge line temperature, not the liquid line.

  10. #10
    Join Date
    Sep 2005
    Location
    florida
    Posts
    5,434
    Quote Originally Posted by mwright View Post
    So take it next to the TXV? The TXV is a bout 10" from the evap coil.
    Yep 6 to 8 '' from the evap coil.
    I love the smell of phosgene first thing in the morning:

    To apply for professional membership click here


    Educational forums are open.

    If you would like to submit a link or an article or other related info to the EF. click here

  11. #11
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    20,921
    Quote Originally Posted by mwright View Post
    Yes I do have the manual thank you

    Model is SC478

    SC Temp is Negative 45 not positive 45
    Measuring SH next to compressor so yes 20 is not bad. Measuring SC just before the condenser coil.
    I am concerned about the high pressure on the high side sorry I don't mention it.


    Is that a typo or did you mean to say that you are measuring the temperature at the inlet to the condenser. At that point in the system, you will have superheated gas as you are supposed to, explaining your 'negative subcooling' reading.

  12. #12
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    20,921

  13. #13
    Join Date
    Feb 2012
    Location
    Savannah, NY
    Posts
    67
    Quote Originally Posted by jpsmith1cm View Post


    Is that a typo or did you mean to say that you are measuring the temperature at the inlet to the condenser. At that point in the system, you will have superheated gas as you are supposed to, explaining your 'negative subcooling' reading.
    Yes between the compressor and the condenser coil but closer to the coil. Am I supposed to Benin the other side of the coil, the output side?

    Incase you haven't figured it out I'm new to this and I appreciate all the help. Where I work doesn't have anyone with the time to train me so I'm digging in and learning as I go. :-)

Page 1 of 3 123 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •