    Quote Originally Posted by Tech Rob View Post
    R123, the truth of the matter is that we're both right! lol

    Thanks for helping me to look at that thing from a different perspective.

    And thanks for your perspective.

    I know you and Jayguy are 2 of the most knowledgable people on this site!

    We all know how the starter works.

  2. #28
    Join Date
    Mar 2007
    Posts
    3,140
    Thanks, and NP



    Group hug
    The key to happiness is lower expectations.

  3. #29
    Join Date
    Aug 2000
    Location
    Austell, Ga.
    Posts
    1,296
    To be precise, the motor will only see an inrush current of exactly 133% of the Full load amps during the wye configaration. Compare that to up to 800% Full load amps when starting Delta or "Across-the Line" start.
    Ain't "None" of us as smart as "All" of us..

  4. #30
    Join Date
    Dec 2002
    Location
    SouthEast NC ICW & Piedmont Foothills
    Posts
    7,635
    Quote Originally Posted by johnnyb View Post
    Can I post my email address here in a thread ?

    in only 2 circumstances:

    1- you want to get the mods attention or spam

    2- it is permitted in the job discussion forum_ONLY

    emails belong in profiles
    It`s better to be silent and thought the fool; than speak and remove all doubt.

  5. #31
    Join Date
    Oct 2011
    Location
    La.
    Posts
    284
    Lets go back to electrical 101. The reason it is refered to as a reduced voltage starter is that the applied voltage passes through multiple windings, thus voltage is dropped at each winding. Hence, the term reduced voltage. Who would have ever imagined that a simple starter would arouse this much traffic.

  6. #32
    Join Date
    Sep 2007
    Posts
    75

    wel put

    this is a quite good and accurate description. As I said , it has been about 12 years since I had ot work on one of theese. I will look Monday and see where the time delay relay is in the circuit. It aslmpost has to be the delay between the two contacgtors on this starter. It was set for 6 minutes. I can't imagine how tnhis worked as a contactor delay on any type of starter.

  7. #33
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    4,533
    Quote Originally Posted by spinning wheel View Post
    Lets go back to electrical 101. The reason it is refered to as a reduced voltage starter is that the applied voltage passes through multiple windings, thus voltage is dropped at each winding. Hence, the term reduced voltage. Who would have ever imagined that a simple starter would arouse this much traffic.
    electrical 101 says that there is voltage drop across ALL windings no matter how many there are in series...1 or 2 or 1000.

    does this mean that all wye wound motors are reduced voltage motors? if i build a motor with 4 windings in series (instead of 2, but of the same total horsepower) will my motor be considered a 'Super Reduced Voltage' motor/starter? will this make my starter have a lower inrush than everyone elses?

    (the answer is no)
    "If you pull one more stunt like you just pulled with Tommy, you won't have to get on a plane because I will personally kick your ass from here to Korea!" - Best of the Best

  8. #34
    Good point Jay

  9. #35
    Join Date
    Jul 2007
    Location
    The Hot South
    Posts
    1,375
    I could make the argument that the wye delta motor/starter is a reduced voltage motor/starter due to the fact that the same motor (and starter) terminals (T1-T4, T2-T5, & T3-T6) see a reduced voltage when connected in wye as opposed when the exact same terminals are connected in delta.

  10. #36
    Join Date
    Jan 2009
    Location
    Not in Iran
    Posts
    1,111
    Quote Originally Posted by Tech Rob View Post
    LOL! Richard, I see what you did there!
    I can't c,
    no signature blast'em man blast'em
    !!!KILL THE TERRORIST!!!

  11. #37
    Join Date
    Mar 2004
    Location
    ottawa canada
    Posts
    2,111
    Quote Originally Posted by R123 View Post
    I've been researching this and it appears to be a matter of semantics as some starter books list it as reduced voltage starters and some don't.
    Potatoes...potatoes... tomatoes...tomatoes...schedule...schedule,,and some pudding just for you Jay .
    The toy chest is officially full ... I got a new toy..... 2007 Aston Martin V8 Vantage
    You bend em" I"ll mend em" !!!!!!!
    I"m not a service tech.. I"m a thermodynamic transfer analyst & strategic system sustainability specialist
    In the garage , greasin', oilin' . tweakin' n shinin' Roll on spring 2015 !!

  12. #38
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    4,533
    Quote Originally Posted by Healey Nut View Post
    Potatoes...potatoes... tomatoes...tomatoes...schedule...schedule,,and some pudding just for you Jay .
    i like pudding!
    "If you pull one more stunt like you just pulled with Tommy, you won't have to get on a plane because I will personally kick your ass from here to Korea!" - Best of the Best

  13. #39
    Join Date
    Oct 2011
    Location
    La.
    Posts
    284

    Smile

    Quote Originally Posted by jayguy View Post
    electrical 101 says that there is voltage drop across ALL windings no matter how many there are in series...1 or 2 or 1000.

    does this mean that all wye wound motors are reduced voltage motors? if i build a motor with 4 windings in series (instead of 2, but of the same total horsepower) will my motor be considered a 'Super Reduced Voltage' motor/starter? will this make my starter have a lower inrush than everyone elses?

    (the answer is no)
    That has nothing to do with the wye delta starter. I believe that you like to hear yourself type at times. Try not to overthink life so much.

Page 3 of 5 FirstFirst 12345 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event