    yes ie is a reduced voltage starter

    with respect to the windings. The applied source voltage is the same but in the y configuration there are two windings in series with each phase of the source which cuts the voltage per winding in half which should cut the power to 1/4. but I do not remember how the math works out in reality and I'm not going to look it up again. Thanks for all the replies , guys. And girls if any of you are girls. (Not meaning you guys are girls)

  3. #43
    Join Date
    Jan 2009
    Location
    Tampa
    Posts
    1,467
    Post Likes
    ,!!!!MEH!!!!,!,!

    #1
    Wye delta uses at least 3, and sometimes 4 contactors, depending on if it's open or closed transition. It's not a reduced voltage starter. It's a full voltage, reduced inrush type of starter.

    #2
    The wye-delta starter has no means of reducing the voltage at the motor terminals. However, the effect on the motor is the same as reduced voltage because in wye, the motor only sees 58% of the line voltage through each winding.*
    Rob

    #3
    a wye delta motor is NOT a reduced voltage motor. it recieves the full voltage (that the building can provide) at all times (except in Open Transition starters).
    jay guy*

    #4

    a wye delta motor is NOT a reduced voltage motor. it recieves the full voltage (that the building can provide) at all times (except in Open Transition starters).

    Most (but not all) VF drives are reduced voltage starters.
    Depending on how you look at it, a Solid State Starter is reduced voltage starter (but not really).
    Primary Resistor is reduced voltage starter.
    MultiPoint Reduced Voltage is a reduced voltage starter.
    Auto Transformer is a reduced voltage starter.

    a wye-delta starter is not a reduced voltage starter. changing the order of the windings does not change the incoming voltage. it does change the resistance and reactance of the motor...but the motor/starter is still full voltage.
    Jay guy

    #5
    I got out some of my motor/starter books and it does say in both of them that it is similar to a reduced voltage starter but does not classify it as a reduced voltage starter, so my apologies. *

    #6
    The reason it is refered to as a reduced voltage starter is that the applied voltage passes through multiple windings, thus voltage is dropped at each winding. Hence, the term reduced voltage. Who would have ever imagined that a simple starter would arouse this much traffic.

    #7
    This is a good explanation of what approach is. But to expand a little, approach tells us how efficient our heat transfer is. A high approach means a poor heat exchange is taking place. Most likely culprit is waterside fouling. a low approach means there was a good heat transfer. An ideal approach is 0 which would mean the heat transfer efficiency is 100%, which is not really possible, but we can get really close

    #8
    the correct formula for inrush current on ac induction motors includes: magnetizing resistance, magnetizing reactance, motor winding resistance, motor winding reactance, rotor resistance and rotor reactance and of course voltage.

    AND THIS IS HOW IT WORKS!
    Thank god ness for this forum, canT find this in a 4 hour class,
    no signature blast'em man blast'em
    !!!KILL THE TERRORIST!!!

  4. #44
    Join Date
    Mar 2004
    Location
    ottawa canada
    Posts
    4,011
    Post Likes
    Lets just call it "reduced inrush " and be done with it . Can we put this one to bed now ??
    The toy chest is officially full ... I got a new toy..... 2007 Aston Martin V8 Vantage and yes it still gives me goosebumps
    You bend em" I"ll mend em" !!!!!!!
    I"m not a service tech, I’m retired ….I used to be a thermodynamic transfer analyst & strategic system sustainability specialist
    In the new big shop , greasin', oilin' . tweakin' n shinin' !!

  5. #45
    Join Date
    Mar 2007
    Posts
    3,824
    Post Likes
    Quote Originally Posted by mlkwal1 View Post
    AND THIS IS HOW IT WORKS!
    Thank god ness for this forum, canT find this in a 4 hour class,
    In the 5 years I've been browsing and posting here, I've learned so much, and I know that I'm a better tech for it. I espouse the virtues of HVAC-Talk to everyone I work with.
    Don't pick the fly crap out of the pepper.

  6. #46
    Join Date
    May 2011
    Location
    North FL.
    Posts
    206
    Post Likes
    I'll second ya both, good stuff - good stuff





    Sent from my iPhone using Tapatalk

  7. #47
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    8,082
    Post Likes
    Quote Originally Posted by Healey Nut View Post
    Lets just call it "reduced inrush " and be done with it . Can we put this one to bed now ??
    reduced inrush works for me!


    type, type, type, type, type, type, type, type, type, type, type, type, type, type, type, type, type, type, type, type, type, type, type, type, type, type, type, type, type, type, type, type, type, type, type, type, type, type, type, type, type, type, type, type, type, type, type, type, type, type, type, type, type, type, type, type, type, type, type, type, type, type, type, type, type, type, type, type, type, type, type, type, type, type, type, type, type, type, type, type, type, type, type, type, type...

    ...didn't want SW to feel left out.
    "Right" is not the same as "Wise".

    Don't step on my favorite part of the Constitution just to point out your favorite part.

    Just because you can measure it, doesn't mean it is important. Just because you can't measure it, doesn't mean it isn't important.

  8. #48
    Join Date
    Jan 2009
    Location
    Tampa
    Posts
    1,467
    Post Likes

    Talking

    HAHA





    doesnt look like bed time.,
    no signature blast'em man blast'em
    !!!KILL THE TERRORIST!!!

  9. #49
    Join Date
    Oct 2011
    Location
    La.
    Posts
    323
    Post Likes
    Thanks for the thought Jay.

  10. #50
    Join Date
    Dec 2009
    Location
    Hotlanta GA.
    Posts
    218
    Post Likes
    OK, I have read this post and now have all kinds of questions, why ----- I have no idea why, I just do .................

    LOVE IT ALL..........

    And to the closing I must add my most understood line from a great person some time ago,

    "I remember when ELECTRICITY, was just electricity!"

  11. #51
    Join Date
    Sep 2004
    Posts
    13,938
    Post Likes
    no it would be a mega super dooper hella reduced electromotive force starter!!!!!

    Quote Originally Posted by jayguy View Post
    electrical 101 says that there is voltage drop across ALL windings no matter how many there are in series...1 or 2 or 1000.

    does this mean that all wye wound motors are reduced voltage motors? if i build a motor with 4 windings in series (instead of 2, but of the same total horsepower) will my motor be considered a 'Super Reduced Voltage' motor/starter? will this make my starter have a lower inrush than everyone elses?

    (the answer is no)
    true knowledge exists in knowing that you know nothing.

  12. #52
    Join Date
    Jan 2008
    Location
    pritzberg
    Posts
    4,641
    Post Likes
    Quote Originally Posted by jayguy View Post
    i like pudding!
    i like nickel never seize, thinned out with some 5gs.
    \m/
    original member of the racoon brotherhood

  13. #53
    Join Date
    Feb 2011
    Posts
    114
    Post Likes
    Quote Originally Posted by jayguy View Post
    Depending on how you look at it, a Solid State Starter is reduced voltage starter (but not really).
    I wonder why you say “but not really”?

    If the electronic switch (gate) is triggered after the cycle peak then it would defiantly seem to be a reduced voltage starter. Even if the switch is triggered before the cycle peak, such that the peak voltage is included in the cycle, the nominal voltage as read by a volt-meter is still going to be reduced.

    I’ve even been toying with the idea of using a solid state starter to send the very tail end of the power cycle to the motor windings of a small hermetic compressor, as a way to eliminate the crank case heater. The windings themselves would become the heater and with the voltage turned low enough the motor itself wouldn’t budge.

    Other than that I agree with your assessment.

  14. #54
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    8,082
    Post Likes
    Quote Originally Posted by dumnut View Post
    I wonder why you say “but not really”? ...
    like i said, it depends on how you look at it.

    during the voltage wave cycle, as the motor is energized, it does recieve a lower than normal voltage signal during the first half of the ramp up...however, about half way in the start up cycle, it recieves the full voltage signal. the SSS just cuts off the voltage wave form at different points in the wave as the chiller comes up to speed. you could say that this was a form of reduced voltage, but i believe that it is a full voltage starter with a wave form modification versus actually reducing the voltage (and giving ith the full wave form) to the motor....this one is a little tricky.

    my main point to all of my arguing was that the unit (motor, starter or motor and starter) recieves full voltage but the unit changes resistance/reactance to gain a lower amperage inrush. while some were saying that it was all semantics, there really are starters out there that reduce the voltage that the motor recieves (without changing the motors characteristics) to achieve the lower inrush.
    "Right" is not the same as "Wise".

    Don't step on my favorite part of the Constitution just to point out your favorite part.

    Just because you can measure it, doesn't mean it is important. Just because you can't measure it, doesn't mean it isn't important.

  15. #55
    Join Date
    Feb 2011
    Posts
    114
    Post Likes
    Quote Originally Posted by jayguy View Post
    like i said, it depends on how you look at it.

    during the voltage wave cycle, as the motor is energized, it does recieve a lower than normal voltage signal during the first half of the ramp up...however, about half way in the start up cycle, it recieves the full voltage signal. the SSS just cuts off the voltage wave form at different points in the wave as the chiller comes up to speed. you could say that this was a form of reduced voltage, but i believe that it is a full voltage starter with a wave form modification versus actually reducing the voltage (and giving ith the full wave form) to the motor....this one is a little tricky.
    Ah, now I see where you are coming from.

    my main point to all of my arguing was that the unit (motor, starter or motor and starter) recieves full voltage but the unit changes resistance/reactance to gain a lower amperage inrush. while some were saying that it was all semantics, there really are starters out there that reduce the voltage that the motor recieves (without changing the motors characteristics) to achieve the lower inrush.
    And I support your efforts to correct that confusion. Some of those posts (at least one) could easily be misinterpreted to give the impression that the delta configuration is far more efficient that the wye configuration, which is simply not true. I think you also touched on that confusion. We owe you a debt of gratitude for your efforts.

+ Reply to Thread
Page 3 of 3 FirstFirst 123

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •