    Traulsen Freezer <No Suction Pressure>

    This is for a Traulsen 2 door Commercial Kitchen Freezer. R502, Suction accum. Cap Tube with a EPR or is it a Cpr? I have not worked on alot of these. My Suction pressure well there is none goes right into a vacuum. Head is about 100 psig. When i shut the unit off it does equalize. Does that eliminate filter drier, cap tube ,suct acc. for a blockage? There is no pressure drop accross any of these items or there would be a temp. Diff felt correct? So i suppose my question would be can the EPR cause this. This unit was offline for 1 month with nothing wrong before that. Then was restarted after the mice issues were attended to in the facility and the BOH gave them the green light. Mickey was found dead in the evap tray. RIP. Any thoughts would be greatly appreciated. See attachment.

    Jp
    Attached Images Attached Images  
    like it love it live it

  2. #2
    Join Date
    Aug 2002
    Location
    Southold.calm
    Posts
    5,582
    What is the high side pressure?

    That is a CPR not a EPR valve and yes it could be stuck closed. Try turning the adjustment screw all the way in.

  3. #3
    Join Date
    Mar 2007
    Location
    wedged in freezer shelf
    Posts
    6,664
    Find and fix the leak
    “If You Can Dodge A Wrench You Can Dodge A Ball”

  4. #4
    Join Date
    Mar 2007
    Location
    wedged in freezer shelf
    Posts
    6,664
    Quote Originally Posted by itsiceman View Post
    Find and fix the leak
    or Find and fix the leaks
    “If You Can Dodge A Wrench You Can Dodge A Ball”

  5. #5
    Join Date
    Nov 2006
    Location
    long island city
    Posts
    111
    what would be a good choice of refrigerant now?
    like it love it live it

  6. #6
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    4,575
    408a
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Liberalism-Ideas so good they mandate them

  7. #7
    Join Date
    Nov 2006
    Location
    long island city
    Posts
    111
    Is there a CPR tool? It`s location is real tight to see inside?
    like it love it live it

  8. #8
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    4,575
    Take off the cap and use an allen key
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Liberalism-Ideas so good they mandate them