Traulsen Freezer <No Suction Pressure>
This is for a Traulsen 2 door Commercial Kitchen Freezer. R502, Suction accum. Cap Tube with a EPR or is it a Cpr? I have not worked on alot of these. My Suction pressure well there is none goes right into a vacuum. Head is about 100 psig. When i shut the unit off it does equalize. Does that eliminate filter drier, cap tube ,suct acc. for a blockage? There is no pressure drop accross any of these items or there would be a temp. Diff felt correct? So i suppose my question would be can the EPR cause this. This unit was offline for 1 month with nothing wrong before that. Then was restarted after the mice issues were attended to in the facility and the BOH gave them the green light. Mickey was found dead in the evap tray. RIP. Any thoughts would be greatly appreciated. See attachment.
Jplike it love it live it
-
03-29-2012, 07:48 AM #2
What is the high side pressure?
That is a CPR not a EPR valve and yes it could be stuck closed. Try turning the adjustment screw all the way in.
-
03-29-2012, 08:00 AM #3
Find and fix the leak
“If You Can Dodge A Wrench You Can Dodge A Ball”
-
03-29-2012, 08:06 AM #4
-
03-29-2012, 08:29 AM #5
Professional Member
- Join Date
- Nov 2006
- Location
- long island city
- Posts
- 105
what would be a good choice of refrigerant now?
like it love it live it
-
03-29-2012, 08:43 AM #6
408a
Local 597 Service Fitter
Metal Trade Journeyman
PAY ME NOW OR PAY ME LATER
It was working when I left...
WWFD
-
03-29-2012, 08:47 AM #7
Professional Member
- Join Date
- Nov 2006
- Location
- long island city
- Posts
- 105
Is there a CPR tool? It`s location is real tight to see inside?
like it love it live it
-
03-29-2012, 09:00 AM #8
Take off the cap and use an allen key
Local 597 Service Fitter
Metal Trade Journeyman
PAY ME NOW OR PAY ME LATER
It was working when I left...
WWFD