    true freezer works....sometimes

    I have been working on a three door true freezer. It will pull down to -20f and a few hours later gets up to 80f. Have not caught it in the act. By the time i get there customer has reset and seems to be working fine. Thought it was sticking in defrost so i replaced defrost control. Got a call back today. Same problem. Any suggestions? thanks

  2. #2
    Join Date
    Feb 2006
    Location
    USA
    Posts
    4,381
    Post Likes
    you check the defrost termination?

  3. #3
    Join Date
    Dec 2007
    Location
    East Coast
    Posts
    29
    Post Likes
    Put it in defrost and see what it gets up to.

  4. #4
    Join Date
    Nov 2007
    Location
    Mississippi
    Posts
    1,571
    Post Likes
    Thread Starter
    I should have already provided this info, but this is a model T-72F. It is located in a mobile catering trailer. There is a three door cooler directly across fron it (cooler condenser blowing into freezer condenser). Exhaust fan does not work in trailer. I think the condenser air is recirculating and overheating compressor in the heat of the day (tripping snap disk on top of compressor). I told customer to open window and put a box fan in the door until ex fan is replaced. Also there is no service taps on condenser skid to check pressures. Condenser coil is clean. Both cond fans operational.

  5. #5
    Join Date
    Feb 2008
    Location
    California
    Posts
    2,091
    Post Likes
    Quote Originally Posted by socotech View Post
    By the time i get there customer has reset and seems to be working fine.
    What is the customer resetting?

    If you find that out, it will lead you to a likely cause...

  6. #6
    Join Date
    Nov 2007
    Location
    Mississippi
    Posts
    1,571
    Post Likes
    Thread Starter
    Customer said when they find the box temp high, the defrost clock green light is lit and cond fans running (I know this doesnt mean the compressor is running). Also the evap fans not running during this time, but Im assuming the fan delay has them out until temp comes down.

  7. #7
    Join Date
    Feb 2008
    Location
    California
    Posts
    2,091
    Post Likes
    that description sounds like an open overload.

    But what is the customer resetting? Could it possibly be a high pressure safety that's inline with the compressor?

  8. #8
    Join Date
    Nov 2007
    Location
    Mississippi
    Posts
    1,571
    Post Likes
    Thread Starter
    Quote Originally Posted by Phase Loss View Post
    What is the customer resetting?

    If you find that out, it will lead you to a likely cause...
    They unplug the main power cord for a while then plug it back in.

  9. #9
    Join Date
    Feb 2008
    Location
    California
    Posts
    2,091
    Post Likes
    defiantly sounds like a tripping overload.

    I'm not familiar with True Freezers...But.

    I would check the CRO if it has one. Also check the starting components.

  10. #10
    Join Date
    Sep 2011
    Location
    Augusta, ME
    Posts
    135
    Post Likes
    Sounds like to me you already have determined atleast part of the problem with the hot air recirculation across the condenser coil.

  11. #11
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    23,572
    Post Likes
    FYI True freezers and Grasslin timers don't get along. Not sure if that is the problem but if you change out the clock again, use a Paragon.
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Why is it that those who complain the most contribute the least?
    MONEY CAN'T BUY HAPPINESS. POVERTY CAN'T BUY ANYTHING

  12. #12
    Join Date
    Feb 2008
    Location
    California
    Posts
    2,091
    Post Likes
    Quote Originally Posted by 2sac View Post
    FYI True freezers and Grasslin timers don't get along. Not sure if that is the problem but if you change out the clock again, use a Paragon.
    Whats the deal with this? I haven't worked on enough of them to know which clock is used more often. But how would the unit know?

  13. #13
    Join Date
    Jun 2009
    Location
    DFW, TX
    Posts
    1,719
    Post Likes
    Quote Originally Posted by 2sac View Post
    FYI True freezers and Grasslin timers don't get along. Not sure if that is the problem but if you change out the clock again, use a Paragon.
    Hmm.. I have to say I disagree, especially since I've started up brand new True freezers with Grasslin timers. All we carry on the truck stock is Grasslin clocks and we have never had a problem with them on True freezers.

    But to your credit, I will say that when you are converting from a Paragon to a Grasslin, the terminal numbers (1,2,3,4,N,X,F) don't match up the same, and it can be a little confusing. The last one it took me a little while to think it through, but after I got it done it worked fine and hasn't had any issues for about a month now.

  14. #14
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    23,572
    Post Likes
    We have had numerous issues with the relays on the grasslins welding shut or stuck open ONLY on True freezers. From what I understand, it happens during the inrush of current on startup. The older True design had a Paragon timer. This is from memory, so forgive me if I'm wrong. When True first changed over to Grasslin, they were wired the same way. After having problems, I believe the factory installed a relay in the electrical compartment. The grasslin timer energizes a relay, and not the compressor directly. If you have a unit without a relay, I'd recommend the Paragon
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Why is it that those who complain the most contribute the least?
    MONEY CAN'T BUY HAPPINESS. POVERTY CAN'T BUY ANYTHING

  15. #15
    Join Date
    Sep 2007
    Posts
    110
    Post Likes
    If it gets down to _20f .. you probably don't have a refrigeration problem , but rather a control probelem. Thermostat sticking, defrtost timer sticking, defrost termination sticking,loose wire, burnig (going bad ) overload on compressor, burning (going bad ) contact on timer. Afew things to check. You may have to baby sit it to catch it. I also do not like the Graslin. The Paragon ued to be "bulletproof" but I think that all of thagt stuff is foreign made now and the foreigners do not have "high quality " in their vocabulary.

  16. #16
    Join Date
    Feb 2008
    Location
    California
    Posts
    2,091
    Post Likes
    Quote Originally Posted by 2sac View Post
    We have had numerous issues with the relays on the grasslins welding shut or stuck open ONLY on True freezers. From what I understand, it happens during the inrush of current on startup. The older True design had a Paragon timer. This is from memory, so forgive me if I'm wrong. When True first changed over to Grasslin, they were wired the same way. After having problems, I believe the factory installed a relay in the electrical compartment. The grasslin timer energizes a relay, and not the compressor directly. If you have a unit without a relay, I'd recommend the Paragon
    Now I got ya, makes scene.

    I do the same to MR4 controllers. (install external relays)

    Good ole mechanical time clocks had nice contacts...these electronic time clocks have crappy relays.

  17. #17
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    14,048
    Post Likes
    Im going with defrost termination switch , or t stat

  18. #18
    Join Date
    Jun 2009
    Location
    DFW, TX
    Posts
    1,719
    Post Likes
    Make sure the self closing door hinges are working. Because something I've often seen is the customer gets in a hurry and the doors don't get shut all the way, this causes the evaporator fans to turn off, and they don't really notice until the box is already at 35*f, although this still doesn't really explain 80*F box temp.

    I agree like everybody else says, probably defrost termination switch is not terminating (or it is, and the timer solenoid or release relay has failed) causing it to stay in defrost for much longer than necessary until box gets so warm.

  19. #19
    Join Date
    Nov 2007
    Location
    Mississippi
    Posts
    1,571
    Post Likes
    Thread Starter
    Just a follow up. I did go and babysit the unit for a few hours and definatly air recirculation problem. Air into condenser getting up to 106 degrees after about two hours of operation and 74 degree ambient. Put a box fan near condenser and it works fine all day. I wonder whats going to happen when its 100+ this summer.

  20. #20
    Join Date
    Mar 2010
    Location
    Lindenhurst, NY
    Posts
    26
    Post Likes

    Exclamation

    Is your compressor hot upon arrival? What happens when your unit goes into defrost?

+ Reply to Thread
Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Tags for this Thread

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •