    Hussman open face cooler problems

    I have a hussman open faced cooler that short cycles all the time. I replaced the thermostat thinking it was defective does the same thing dropped charge and weighed in 32 oz 134a still short cycles. the only way i can get this cooler to stop short cycling is i installed a new thermostat instead of mounting it on the coil i ran it to the top of the cooler set it at 40 degrees and it seem to run fine what do you think?

  2. #2
    Join Date
    Feb 2008
    Location
    California
    Posts
    2,066
    It used to work right?

  3. #3
    yes it used to work right

  4. #4
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    4,680
    Is it the correct thermostat you are trying to replace it with? Also, if it's sensing coil temp and the valve is not feeding properly it's not going to work right. Fans working correctly? Honeycombs clean?
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Liberalism-Ideas so good they mandate them

  5. #5
    Same t-stat this is a fixed orfice so no expansion valve feeding all fans running clean evap clean condenser. i guess my question is why does this thing run on coil temp if there isnt an expansion valve why cant it run off box temp? I never understood that.

  6. #6
    Join Date
    Oct 2008
    Posts
    813
    Quote Originally Posted by HeinzHVACR View Post
    Same t-stat this is a fixed orfice so no expansion valve feeding all fans running clean evap clean condenser. i guess my question is why does this thing run on coil temp if there isnt an expansion valve why cant it run off box temp? I never understood that.
    Why coil sensing tstat? My guess is because it's an open faced. I take it that's another name for an air curtain cooler. Either way, there's outside air always coming in.

    Aside from walk-ins, I usually see R/I coolers (with doors) or sandwich/pizza prep tables coolers. The benefit I see for having a coil sensing tstat is it's nearly impossible to cause a freeze up of the evaporator coil. With a cabinet tstat, if a door is left open, it will remain in a cooling cycle endlessly, causing a freeze up. A frozen evaporator will further perpetuate that since airflow is blocked. The cabinet tstat would never be satisfied.


    "You never know what others don't know." -

    If I can't laugh at myself...then I'll laugh at YOU! -

  7. #7
    Join Date
    Jul 2000
    Location
    Guayaquil EC
    Posts
    10,421
    Quote Originally Posted by HeinzHVACR View Post
    I have a hussman open faced cooler that short cycles all the time. I replaced the thermostat thinking it was defective does the same thing dropped charge and weighed in 32 oz 134a still short cycles. the only way i can get this cooler to stop short cycling is i installed a new thermostat instead of mounting it on the coil i ran it to the top of the cooler set it at 40 degrees and it seem to run fine what do you think?
    You're probably going to have coil icing problems by doing that, but it's difficult to say since you haven't told us exactly what case you have there.

    From what you've said I would assume this is a self-contained vertical merchandiser likely similar to the GSVM:

    http://www.hussmann.com/Installation...ls/GSVM_im.pdf

    Is that it? Post the model number and we'll be much better able to help you out here.

  8. #8
    GSVM -4072

  9. #9
    Join Date
    Jul 2000
    Location
    Guayaquil EC
    Posts
    10,421
    Quote Originally Posted by HeinzHVACR View Post
    GSVM -4072
    Pretty good guess, eh?

    The GSVM-4072 is designed to have a coil sensing temperature control set at 19F to 21F to maintain between 35F and 40F average case temperatures.

    It the airflow has been compromised by dirty buildup, as was mentioned it may be just a matter of cleaning out the crap. If the original control was actually OK, short cycling would be a typical symptom of reduced airflow with a coil sensing t'stat.

  10. #10
    Join Date
    Sep 2010
    Location
    miami,fl.
    Posts
    639
    Quote Originally Posted by icemeister View Post
    Pretty good guess, eh?

    The GSVM-4072 is designed to have a coil sensing temperature control set at 19F to 21F to maintain between 35F and 40F average case temperatures.

    It the airflow has been compromised by dirty buildup, as was mentioned it may be just a matter of cleaning out the crap. If the original control was actually OK, short cycling would be a typical symptom of reduced airflow with a coil sensing t'stat.
    daaam icemeister your a beast in the refrigeration trade. ive read alot of threads and you post alot of good info,

  11. #11
    Join Date
    Jul 2002
    Location
    SE Texas
    Posts
    450

    Thumbs up

    Quote Originally Posted by anthonyac1 View Post
    daaam icemeister your a beast in the refrigeration trade. ive read alot of threads and you post alot of good info,
    With your chrome heart shining in the sun, long may you run.

  12. #12
    Join Date
    Sep 2005
    Location
    florida
    Posts
    5,514
    Quote Originally Posted by anthonyac1 View Post
    daaam icemeister your a beast in the refrigeration trade. ive read alot of threads and you post alot of good info,
    Quote Originally Posted by SandShark View Post

    When I grow up I want to be just Like ice.
    I love the smell of phosgene first thing in the morning:

    To apply for professional membership click here


    Educational forums are open.

    If you would like to submit a link or an article or other related info to the EF. click here

  13. #13
    All evaporator fans are running air flow is great I have two other units that are exactly the same in a row next to it and keeping temperature this one runs gets close to 40 degrees then shuts off then 30 seconds later it tries to come back on but it doesnt come on because it just shut off it sounds locked up until it resets after a minute or so start components are working as normal I justed checked on the unit and the thermostat that controls the box works great for now it really does the same thing because the defrost is timed and there isnt an expansion valve

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event