03-27-2012, 07:20 PM #1
Motor with VFD runs hot, 170*f
Motor with VFD runs hot, 170*f.
Cutler hammer AFM15100B. 575 volt, 3ph, 10hp
10.4 amp motor, 10 hp motor.
Measured input voltage at 592, output voltage at 650, running at full speed, 60 hz, 10.6 amps.
When speed drops to 56 hz, amps are 9.6, output volt are 643.
Blows one fuse, the same fuse after some 3 hours of run time.
Volt to hertz ratio set to high? Customer says no one has touched anything.
I'll need to go back with a manual.
Any thoughts?ENJOY THE RIDE
-
03-27-2012, 08:25 PM #2
is the motor and VFD new items since install.is the VFD rated for that motor in Volts and HP maximum off tag?the motor is 170F or the VFD cabinet is?if the motor is old and the VFD was installed as add on?are the fuses before the VFD or between the VFD and motor?if the motor is older having run 60Hz since install now the windings are seeing voltages above tagged nameplate as the amps drop in inversion ramping....is it just a soft start or are you doing VAV static supply air to setpoint.how far is the VFD from the motor...is the VFD vented or cooled in anyway besides just the MER
"when in doubt...jump it out" http://www.youtube.com/watch?v=aMy-sAHwS4E
-
03-27-2012, 10:52 PM #3
Motor and vfd have been there for years.
Motor is 170*f.
Power goes through starter before the vfd. Power goes through the contactor part, then to the vfd, back to the starter into the overloads and to the motor.
Vfd and motor are 15 feet apart.
Vfd responds to static pressure.ENJOY THE RIDE
-
03-28-2012, 05:56 AM #4
Moved to Tech to Tech
-
03-28-2012, 08:30 AM #5
Regular Guest
- Join Date
- Feb 2012
- Location
- Upstate SC
- Posts
- 84
Not saying that your problem is here, but I have never seen a VFD that also required a starter and heater.
-
03-28-2012, 05:38 PM #6
-
03-29-2012, 12:01 AM #7
I would recommission the drive, no doubt about it.
Who knows maybe someone was curious and changed a parameter by mistake and doesn't want to say.
Make sure the switching frequency is not se too high on the VFD.
Also, get rid of the starter and its OLs, the VFD already handles those duties. They aren't rated for VFD voltages anyway - not good!Last edited by RuralSpaceman; 03-29-2012 at 12:06 AM. Reason: thought of something else.
-
03-29-2012, 03:01 AM #8
If the motor is rated 575VAC @ 60Hz, the drive should provide 575VAC @ 60Hz. Usually a motor accepts a +/- 10% variation in input voltage which would be 632VAC. You measured 650VAC. If you apply slightly higher voltages to a motor the amps decrease. Your motor read the maximum amps with higher voltage. This could be an indication of increased mechanical load on the shaft (controlled pressure above design?). I think it is worth to check the motor settings in the drive (Depending on them the drive sets the V/f ratio which do not really fit in your case.) and whatever is attached to this motor.
"Quality exists, when the price is long forgotten."
Henry Royce
-
03-29-2012, 05:51 PM #9
you mentioned blowing a fuse but you have a starter?maybe somebody can kick in here are you pulling inverted voltages thru a starter?the VFD itself is an overload protection.i have seen slow-blow fuses and a 3 phase contactor supply a VFD and called a power contactor with Trane units.the 3 phase out of the VFD should go to the load not an overload device!
"when in doubt...jump it out" http://www.youtube.com/watch?v=aMy-sAHwS4E
-
03-29-2012, 05:57 PM #10
FLA 10.4 "or" SFA 10.4 ?
and the drive is programmed for which?
-
03-29-2012, 10:12 PM #11
Customer had me replace the motor. He had no interest in checking out the vfd or removing the starter. He said no one has touched the vfd and the starter has been there for years. So it has to be the motor. New motor is still to hot to touch. Everything else was the same when I left. So now he'll call to say it broke again, never call me again in embarrasment, or it actually works. Either way I had him sign off to say he accepts all outcomes, good or bad.
ENJOY THE RIDE
-
03-30-2012, 12:27 AM #12
You can lead a horse to water...