    Siemens Integration

    I'm working on a BACnet chiller integration into a Siemens control system and am needing the application builder and firmware loading tool to get my points in the BAS. Anyone out there have a copy they could forward onto me?

    Thanks!

  2. #2
    Join Date
    Sep 2007
    Posts
    150
    Those are tools that are Siemens only. You wont be able to get the licenses

  3. #3
    Join Date
    Oct 2005
    Posts
    309
    Another example of how open BACnet is!

  4. #4
    Join Date
    Sep 2006
    Location
    EU
    Posts
    161
    First, which Siemens system are you working with? There are two current systems (Desigo and Apogee) and at least half a dozen legacy ones.

    Second, why do you think you need all those tools to integrate chiller?

  5. #5
    Join Date
    Dec 2011
    Posts
    39
    It is for an Apogee system with a PXC Modular controller with P2 and BACnet. These tools are required to build the application and add it to system profile to view the points. The application has to be built and then loaded into the controller for use in Insight.

  6. #6
    Join Date
    Sep 2006
    Location
    EU
    Posts
    161
    I'm sorry, I don't know much about Apogee.

    Anyway, if you would like to add new chiller with existing BACnet controller inside, I don't understand, why you need to build an application and load it into some controller.
    All BACnet scada systems I worked with could discover BACnet points directly from the chiller. Then all you need to do is to build some graphical display and that's it. OK, maybe setup some histories, alarms and schedules -- and BACnet is really good in it.

  7. #7
    Join Date
    Dec 2006
    Location
    What? Who? Where?
    Posts
    1,382
    Quote Originally Posted by tlp261 View Post
    Another example of how open BACnet is!
    You're an a*****e. How does Siemens' proprietary software implementation have anything to do with BACnet.

    kontrol out
    "Can't we all just get a Lon?" - Garry Jack
    "BACnet: integration or interrogation?" - The Janitor
    "Open protocols? You can't handle open protocols!" - Nathan R. Jessup
    “What’s that? Aaa… open protocols? Don’t talk about…. open protocols? Are you kidding me? Open protocols? I just hope we can hardwire an interface!” - Jim Mora http://www.youtube.com/watch?v=U7fjDS0jKiE

  8. #8
    Join Date
    Jul 2007
    Location
    Mount Airy, MD
    Posts
    7,100

  9. #9
    Join Date
    Jan 2008
    Location
    Front Range
    Posts
    33
    Zep913,

    You may be better off having your customer purchases the BACnet Client option for Insight.Then add a BACnet MSTP to IP router between the the chiller and Insight. This would allow you and your customer more options for BACnet expansion in the future and avoid having to have the app builder tool needed to make the PXCM a proprietary BACnet gateway.

  10. #10
    Join Date
    Dec 2011
    Posts
    39
    So instead of buying a PXC with bacnet capabilities I would have them buy the single site bacnet license for insight and set up a new bacnet bln. If I went with bacnet IP instead of MSTP then I could avoid the router correct? I haven't had much experience with setting up the bacnet in insight.

  11. #11
    Join Date
    May 2002
    Location
    Baton Rouge, Louisiana
    Posts
    3,616
    Quote Originally Posted by kontrolphreak View Post
    You're an a*****e. How does Siemens' proprietary software implementation have anything to do with BACnet.

    kontrol out
    Good call phreak

    I can't get into an Invensys Jace without their software


    Does that mean Jaces aren't open?
    Dad's Hideout The online mancave for dads

  12. #12
    Join Date
    Jan 2003
    Location
    USA
    Posts
    1,287
    Quote Originally Posted by joey791 View Post
    Good call phreak

    I can't get into an Invensys Jace without their software


    Does that mean Jaces aren't open?
    LOL another day in controls. So just because it says lon or bacnet don't expect to get in and have your way.

    All we can do is call them out......
    Propagating the formula. http://www.noagendashow.com/

  13. #13
    Join Date
    Jan 2008
    Location
    Front Range
    Posts
    33
    Zep913,

    With the Insight BACnet client option you can add a BACnet BLN and use BOB Siemens (BACnet Object Browser ) to discover and add new BACnet devices and points. If your chiller is BACnet IP ready then skip the MSTP to IP router. Unless you have had experience with upgrading and or installing options for Insight you would be better off having the BACnet client option set up for the customer by Siemens. Once the BACnet client option for Insight has been installed then using BOB is pretty straight forward and easy to use.(Discover devices and add BACnet objects to database. If you have a spare LDO ,LDI and LAO available on a existing Siemens controller near the Chiller then I would always try to utilize a hardwired input and output for (enable, status and setpoint )for direct control. I find that sometimes software integration with equipment is best left for all the whistle and bell points.

    Regards,

    Debug