    Carrier 19xl

    I have a carrier 19xl and after start up this year the condenser is sweating during weekend off cycles is it possible the float is stuck?

  2. #2
    Join Date
    Mar 2012
    Location
    montreal/canada
    Posts
    93
    Post Likes
    Do u mean the bottom part of the cond shell and the Liguid line going for the cooling of the motor

  3. #3
    Join Date
    Jun 2010
    Location
    U.A. (upper Alabama)
    Posts
    1,101
    Post Likes
    You said in the off cycle right? Probably your float is closed because there is not any high press. gas going under the float. This holds a level in the condenser and if you have chilled water flowing it transfers the "cold" to the refrigerant in the condenser.

  4. #4
    Join Date
    Mar 2012
    Posts
    3
    Post Likes
    Thread Starter
    sorry only the cond was sweating about half way up. it was sweating bad enough that we needed to mop up the floor beneath it several times. it was just overhauled 2 seasons ago and we have never seen this before. CHW pump was on with a 45 loop CW pump was off with 70 water

  5. #5
    Join Date
    Aug 2009
    Location
    Prattville, Alabama
    Posts
    3,228
    Post Likes
    Was the chill water pump also running those times in the past when you had "never seen this before"?

  6. #6
    Join Date
    Mar 2012
    Posts
    3
    Post Likes
    Thread Starter
    Yea the loops are tied together so we always run the pump with the other chiller

  7. #7
    Join Date
    Oct 2011
    Location
    La.
    Posts
    325
    Post Likes
    That is your problem, the refrigerant is at 45 degrees or whatever your chiller loop is at. This is normal if you run water through it. If it bothers you insulate the botom of the condenser or cool your machine room.

  8. #8
    Join Date
    Aug 2009
    Location
    Prattville, Alabama
    Posts
    3,228
    Post Likes
    Maybe you never saw the sweating in the past because when you looked at the chiller after shutdown, enough time had passed that the refrigerant in the condenser had all migrated to the cold evaporator, and the now empty condenser had warmed to room temperature. If you have multiple chillers, and are pumping chill water through an idle chiller, you are wasting energy. And at times, may be running an additional chiller when it is not really needed.

  9. #9
    Join Date
    Sep 2010
    Location
    San Francisco Bay Area
    Posts
    16
    Post Likes
    Spinning wheel is correct but insulating the barrel is not the answer. The correct course of action is to install an automatic isolation valve (assuming there is none) on the CHWS line of each cooler. This will stop the chilled water from flowing through the lag chiller preventing the condensation from forming. It will also increase the overall efficiency of the plant by preventing the short circuiting of CHWR into the CHWS through the lag chiller.

    If the machine does have an automatic CHW valve, then check it and find out why it isn't closing when the chillers off.

  10. #10
    Join Date
    Mar 2012
    Posts
    7
    Post Likes
    Based on my experience, normally Condenser shell would be insulated by 1/2. By insulating 1/2 of the condenser shell will solve the issue.

  11. #11
    Join Date
    Jun 2009
    Location
    Ancaster,Ontario
    Posts
    27
    Post Likes
    Curious what the condenser refrigerant temp is when this is happening. Also you said it sweats when off for the weekend..does this mean its still sweating after a couple of days being idle? XL's are prone to "sticky" floats but typically shows up when she's running..fluctuating motor current etc..refrigerant MUST be transferring from cond for this to happen.