Checking for condesner coil operation.. How to??
Hey all,
Ive been a service tech for about 1 1/2 years now and I'm stating to do alot more commercial work. My question is sometimes I run into calls like customer says isn't keeping up all the time etc.
Say its a Cap tube system, how do I check for sub cooling if it doesn't have a service port on the liquid line? Can I put a pipe clamp on the hot vapor line leaving compressor atleast 8 inches away to stay away from excess compressor heat and pipe clamp after condenser coil and see drop across?
What is average drop if you can do that? If its a triple rolled or double rolled hard to tell if its moving enough heat out. How do you check that? Is there another way to make sure condenser is moving heat out like it should? Besides looking at pressures...
One more question how do you know what pressures should be besides checking subcooling/superheat?
-
04-13-2012, 12:50 AM #2
New Guest
- Join Date
- Feb 2009
- Location
- Seattle
- Posts
- 4
liquid pressure = discharge pressure on most small systems.
Check charge by superheat for (most)cap tube systems.
Check charge by subcooling for (most)txv systems.
Liquid temperature is checked at outlet of condensing coil for subcooling measurement.
Allow system to run for 15 minutes before making any assumptions.
Typical AC or HP systems you should see a 100# difference in suction to discharge.
-
04-13-2012, 05:55 AM #3
Regular Guest
- Join Date
- Jun 2011
- Location
- NJ
- Posts
- 14
check delta-t across condenser coil.
-
04-13-2012, 03:35 PM #4
All condenser coils are dirty. Clean them.
Local 597 Service Fitter
Metal Trade Journeyman
PAY ME NOW OR PAY ME LATER
It was working when I left...
WWFD
-
04-13-2012, 06:58 PM #5
New Guest
- Join Date
- Aug 2009
- Posts
- 2
How' often do they do tune up/ clean up. Check evaporator
-
04-13-2012, 07:24 PM #6
-
04-13-2012, 07:48 PM #7
Originally Posted by 2sac

Paying particular attention to the ones that need to be split apart to clean.
If you don't they aren't clean.
-
04-13-2012, 08:06 PM #8
Professional Member
- Join Date
- Sep 2006
- Location
- Ohio
- Posts
- 354
If the unit doesn't have a liquid line access valve to get the sub cooling, you can measure the discharge superheat. Take the discharge pressure, convert it to temperature, take the discharge line temperature within 6" of the compressor and do the math.
-
04-17-2012, 12:51 AM #9
Regular Guest
- Join Date
- Apr 2012
- Location
- So. Fl.
- Posts
- 55
Hi Skidoox, I would Check ambient temp. at intake of cond.
& check disch. Air leaving condenser. Should be 20'-30'
Differance. Then check temp. Of liquid line leaving condenser,
Now convert discharge pressure to temp.(saturated cond.
Temp.) this will be your subcooling. I personally like to see
A balance of 10-15'. Hope this helps out.