    Compressor terminals

    I took a look at this Friday afternoon. The in house guys think they lost the refrigerant charge here. Can this be fixed? Compresser ia a Copeland 6RN2-3000-TSK.
    Attached Images Attached Images  
    Local 47

  2. #2
    Join Date
    Feb 2010
    Location
    Ontario Canada
    Posts
    1,339
    I would think a call to Copeland would be in order. I had a Bitzer compressor leak through the terminals and they had a kit to fix the problem.
    good luck.
    Never give up; Never surrender!

  3. #3
    Join Date
    Nov 2004
    Location
    Western NY
    Posts
    943
    Yes it can be fixed, buy a terminal kit,quote him 8 hours worth of labor and follow torque recommendations, they snap with ease.

  4. #4
    Join Date
    Sep 2003
    Location
    Western PA
    Posts
    1,242
    Thanks guys.
    Local 47

  5. #5
    Join Date
    Aug 2010
    Location
    Dearborn MI
    Posts
    26
    Targetman,
    We sell the terminal block already built ready to install. Just take the wires off the inside of the old plate and make sure you put them back on the correct terminal of the new plate. A word of caution though. Many times when we sell a terminal block to replace one that looks like yours, the motor windings burn out shortly after it is put back in service. You should make your customer aware that it could happen.

  6. #6
    Join Date
    Feb 2004
    Location
    New Mexico
    Posts
    4,682
    Quote Originally Posted by remanworld View Post
    Targetman,
    We sell the terminal block already built ready to install. Just take the wires off the inside of the old plate and make sure you put them back on the correct terminal of the new plate. A word of caution though. Many times when we sell a terminal block to replace one that looks like yours, the motor windings burn out shortly after it is put back in service. You should make your customer aware that it could happen.
    Yup, in fact almost for sure.
    Tracers work both ways.

  7. #7
    Join Date
    Nov 2004
    Location
    Western NY
    Posts
    943
    why would the windings burn?

  8. #8
    Join Date
    Mar 2007
    Location
    Home of the newly wed and the nearly dead
    Posts
    2,938
    Replacing the terminals, terminal o-rings, terminal plate gasket, or the terminal plate itself does not make the motor any more likely to burn. What will burn the motor out is a poor connection on the terminal that drops enough voltage to create a single phase or voltage/current imbalance condition. By the uniform discoloration on the buss bars from T4-T7, T5-T8, and T6-T9, as well as the discolored lug on T1, it looks like you already had overloading, bad connections, and/or loose wires. Look how the plastic card in between the motor terminals and the winding temp sensor terminal plate is all burnt. In my experience, this is one of the things that causes terminal o-rings to leak. The terminal swells up from the heat and expands the o-ring. When the terminal cools back down, the o-ring does not fit tightly around the terminal.
    Truth is still truth, even if no one believes it. A lie is still a lie, even if everyone believes it.

    "It's called the american dream because you have to be asleep to believe it" -George Carlin

    "A nation of sheep begets a government of wolves" -Edward R. Murrow

    "I have problems just like you. One time, my dancing horse almost fell into my car elevator" -Mitt Romney

    Buy american made goods & support locally owned businesses!

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •