pump down solenoid
In refrigeration units with remote condensors we have a liquid line solenoid for pumping all of the refrigerant into the liquid reciever to prevent flooding the compressor with liquid refrigerant during start-up when colder than box temperature ambient conditions exist. My question is why don't we see this with heat pumps? These conditions would exist a lot more often, almost everyday during heating season, yet I have only seen a few liquid line solenoids in residential hvac, and they were for long line set runs to prevent so much pressure being put on the compressor during start-up.
-
03-24-2012, 01:55 PM #2
I would like to hear more on this as well... Most heat pumps have crankcase heaters, but that doesn't take care of the liquid in the coil.
-
03-24-2012, 02:05 PM #3
Professional Member
- Join Date
- Jun 2003
- Posts
- 3,633
Most heat pumps have accumulators (or one built into the compressor like trane)
-
03-24-2012, 02:40 PM #4
Professional Member
- Join Date
- Jan 2010
- Posts
- 4,405
-
03-24-2012, 03:06 PM #5
Suction accumulator prevents liquid from entering the compressor, unless of course there's an overcharge.
Refrigeration systems I've seen mostly have the solenoid on the outlet of the evaporator, and close from the stat. Then the pressure cntrl turns off the compressor. Ergo-any liquid stays in the evap. and changes to gas when the sol. v. opens, and rising pressure makes the pressure sw., restarting the compressor.Tom D. - Long-time Journeyman from CT.
On account of being a democracy and run by the people, we are the only nation in the world that has to keep a government four years, no matter what it does.
-
03-24-2012, 09:53 PM #6
-
03-24-2012, 10:06 PM #7
-
03-25-2012, 01:23 AM #8
I hope not to take away from the OP but I run into some Carriers from maybe 15 years ago that have a solenoid in the condenser. If I remember correctly they simply opened and shut with the thermostat as well as the contactor and had nothing to do with pumping down the system.
I can't say I ever did figure out what use they had.
-
03-25-2012, 02:25 AM #9
Professional Member*
- Join Date
- May 2008
- Location
- Myrtle Creek. Oregon
- Posts
- 182
in 50 + years I have never seen it eather.
a stupid question is a question you wont to ask, but don't
-
03-25-2012, 12:30 PM #10
What you have said would work. The trick is to keep liquid from migrating out of the evaporator into the suction line during cold winter days. I have mostly seen them on the liquid line leaving the condensor but have ran into them at the evaporator but can not really remember exact placement, but yours sounds correct to me.
-
03-25-2012, 12:34 PM #11
-
03-25-2012, 12:41 PM #12
-
03-25-2012, 01:39 PM #13
No return.