Page 4 of 5 FirstFirst 12345 LastLast
Results 40 to 52 of 54
  1. #40
    Jan 2011
    Quote Originally Posted by AiResearch
    Movable diffuser in discharge area = Westinghouse / McQuay
    And your point is?
  2. #41
    Mar 2011
    East Coast FL
    My point is only that it was developed by Westinghouse.
    Cheers
  3. #42
    Quote Originally Posted by murphman View Post
    ...Map loaded again, although it did back down at that time.....until map loaded up again.
    it sounds like many here think that a full surge map is bad...it isn't. you want it full. the map is a road map of where NOT to go. it is a map of tested areas that are not fun and to stay away from. the only time it is bad is if the map is full of bad data...surges that occured due to some inaccurate data or some condition that no longer exists like air in the chiller or low condenser water flows...something major like that.
    The weak aren't destroyed by the strong.
    The weak are destroyed by the under-estimated.
    I know a famous song that ends in 'my nose'. The artist is dead. Know who?
  4. #43
    Apr 2012
    So. Fl.
    Hi guys, bklyntek, going bck a few posts, is York's VGD point on chiller similar to carrier's.
    Just asking for clarification, seen carriers w/diffuser wall sensor. But at the was a new to the big iron systems, haven't worked on Carr. Chillers since. Seen more YCAS/R/W's and alittle of the MCQUAY units. I always try to keep to basic principles and has helped me tremendously over the years. Thanks again,it's always a pleasure.
  5. #44
    Jan 2011
    Not sure what the question is Bklyntek. The purpose of the diffuser in the York high pressure centrifugal is to keep the compressor out of the stall zone. Transducer in the discharge measures slight pulsations in the discharge pressure and based on an algorithm moves the diffuser to narrow the gap for gas exiting the compressor.
  6. #45
    North Carolina
    Yep, several chillers with TM2 removed and retrofitted with new vfd's. Tower water consistently around 65-68, but do run low load from time to time. Surge maps detecting surges but seem to be stalls more than surges.
    Is the surge sensitivity set to low, also do your cooling tower fans have drives on them, if so are they holding a consistant condenser water temp or are they hunting? Everything in the system needs to be steady, no abrupt changes for the machine to run smooth.
  7. #46
    Apr 2009
    No drives on tower .
  8. #47
    Jan 2011
    Optiview or single line panel? Like Chad says set sensitivity to 7000.
  9. #48
    I believe email/ westinghouse could have developed the movable diffuser, not that easy to set though back in the day, also think a lot of the problems could have been due to the float system, have seen a few retrofitted to PO.
    With the use of electronics etc maybe hopefully someone improving design.
  10. #49
    North Carolina
    Do you have a condenser water bypass valve?
  11. #50
    Apr 2009
    Sensitivity already at 7000, no condenser bypass valves, no drive on tower fan and yes there is obviously some hunting on tower temps without drives. Is that alone enough to not let drive back off??? Optiview panel exists.
  12. #51
    North Carolina
    Hmm
    [QUOTE=murphman;13109541]Sensitivity already at 7000, no condenser bypass valves, no drive on tower fan and yes there is obviously some hunting on tower temps without drives. Is that alone enough to not let drive back off??? Optiview panel exists.[/QUOTE
    You may already know this but here goes, The chiller is going to try to drive the vanes open to 100% and then back the motor frequency down to a minimum of 30 hz to control setpoint, Although I have never seen one run at 30 hz that is the minimum. In low load situations when the drive has backed down as low as it can without surging it will have to shut the vanes to keep from overshooting the setpoint. When the chiller is running at low load the cooling tower can typically give you colder water than desired (condenser water setpoint should be 14 degrees above chilled water setpoint), so in your case the cooling tower fan cycles. When the chiller is running right on the surge line and then it gets a relativly fast change in condenser water temp it will not have time to react and probably surge. This is why you need to keep the condenser water temp steady or else you will fill the surge map up fast.
    One thing you can try that may work ok is to adjust the surge margin from 0 hz to 2 or 3 hz. This will make the drive run less efficient but will give the chiller more time to react before it surges and creats a surge point. Obviously the better fix would be put a drive on the tower and keep the condenser water temp steady but trying to talk a customer into spending more money can sometimes be difficult.
    Good Luck
  13. #52
    Apr 2009
    Appreciate the help.