    York R123 Cleanup

    Working on york R123 chiller at moment, this machine open for sometime ( due to customer not approving works) , just briefly I usually install driers across cooler/evap, utilising high side pressure for movement across driers.

    Anyone got any better ideas??

  2. #2
    Join Date
    Jan 2011
    Posts
    1,173
    Clarify please. The refrigerant was removed and system was opened and left open for how long? Was it at least covered with plastic with an N2 purge?

  3. #3
    Join Date
    Jan 2009
    Location
    Keokuk, IA
    Posts
    5,520
    What was left open? Just the waterside? What was broken on the chiller? Leaving the refirerant side exposed to the atmosphere is one of the worst things you can do to a chiller... or rather pretty much any refrigerant based cooling system. Main concern in my mind is the compressor bearings rusting. Then the inlet guide vanes rusting and their linkages. Finally rust inside the shells can cause heat transfer issues in the future as the rust comes off and gets bonded to the copper tubes. We just retubed a chiller at my work due to this issue.... that can run as hgih as $60k on a 350T chiller.

  4. #4
    Join Date
    Jan 2009
    Location
    Keokuk, IA
    Posts
    5,520
    Was the unit previously full of water? To dry it out, just pump it down. We even hooked up a small circualtion pump and ran it through a couple 5 gallon 120VAC residential water heaters to get some heat on the unit to help boil off the water. IF it was flooded, just give it a few weeks running that way.

  5. #5
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    4,389
    Quote Originally Posted by rover View Post
    Working on york R123 chiller at moment, this machine open for sometime ( due to customer not approving works) , just briefly I usually install driers across cooler/evap, utilising high side pressure for movement across driers.

    Anyone got any better ideas??
    use a zuggiebeast.

    http://hvac-talk.com/vbb/showthread.php?t=1075381
    When I am late for work, I usually make up for it by leaving early.

  6. #6
    Join Date
    Mar 2004
    Location
    ottawa canada
    Posts
    2,063
    Quote Originally Posted by jayguy View Post
    The Zuggiebeast runs on pudding and lots of it
    The 64 roars to life Whoo hoo ...shes a rolling chassis .
    You bend em" I"ll mend em" !!!!!!!
    I"m not a service tech.. I"m a thermodynamic transfer analyst & strategic system sustainability specialist
    Best Austin Healey In Show twice in 2013 .....All those hrs paid off .

  7. #7
    Join Date
    Aug 2000
    Location
    Austell, Ga.
    Posts
    1,296
    The last I heard the ex-Carrier guy that came up with the "Zuggie-Beast" was working with Refi-Max out of the Regional office in Smyrna Ga. Albeit I believe he resides in Florida. I had him do a couple of chillers saving a few tons of 134 with that "Creation" of his towed behind his truck on a huge trailer. On one chiller He managed to clean the 4000# charge whilst the chiller was running in one day.....
    Da' "Zuggie-Beast" is a wonder to behold.
    Ain't "None" of us as smart as "All" of us..

  8. #8
    Join Date
    Feb 2010
    Posts
    81
    Refrigerant was previously removed, waterside drained (we are not looking at tube failure), there will be no issues with igv or comp bearings, nitrogen was purged and heat lamps utilised at vessels, client sat on repairs to long, now we have go ahead to get chiller running.

    Have had this issue in past, and have used filters at cooler vessel to clean up system, also meant a lot of oil filter changes as well though, was just seeing if any other suggestions were out there.

    This is the 2nd time in 10-18 years same site, have been told to teardown, inspect,repair (having being told a new chiller is in their budget).

    Then client argues cost of filter changes etc to get a chiller running again that has sat idle for 6-8months.

  9. #9
    Join Date
    Jan 2011
    Posts
    1,173
    If you have taken the precautions stated then I wouldn't know where all the "dirt" would be coming from. When the machine is put back together and evacuated properly I think you should be fine. The only time I have ever put a cooler clean up kit on a York YT is when the system took on water though a tube failure.

  10. #10
    Join Date
    May 2011
    Location
    North FL.
    Posts
    206
    Quote Originally Posted by RichardL View Post
    The last I heard the ex-Carrier guy that came up with the "Zuggie-Beast" was working with Refi-Max out of the Regional office in Smyrna Ga. Albeit I believe he resides in Florida. I had him do a couple of chillers saving a few tons of 134 with that "Creation" of his towed behind his truck on a huge trailer. On one chiller He managed to clean the 4000# charge whilst the chiller was running in one day.....
    Da' "Zuggie-Beast" is a wonder to behold.
    RichardL are you talking about Mike Britt ???


    Sent from my iPhone using Tapatalk

  11. #11
    Join Date
    Aug 2000
    Location
    Austell, Ga.
    Posts
    1,296
    Henpeck'..Yes I is...Sharp Dude he is..
    Ain't "None" of us as smart as "All" of us..

  12. #12
    Join Date
    Oct 2011
    Location
    South Georgia
    Posts
    68

    Cool

    Richard, he cleaned up a 19EA burn out for me a few years ago. Took him longer to set it up than the actual cleaning. The refrig sample came back as virgin R-12.

  13. #13
    Join Date
    May 2011
    Location
    North FL.
    Posts
    206
    Yes he has it together, i could go on for days with some of equipment he's designed and built. I started to reply to another thread with " I know a guy" ... Haven't been in a lot of years but he has a shop that's was off the chain in the early 90's. Outstanding person altogether.


    Sent from my iPhone using Tapatalk

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event