Cleaning and maintaining condensate drain lines
I havea question regarding cleaning and maintaining (somewhat) long pipe runs for condensate drains in walk-in coolers. Yesterday I was cleaning coils at my market and noticed the water I was spraying on the coils was draining slowly from the pan.There were a couple clean outs installed in the condensate drain and I removed the plugs and flushed with hot water through a garden hose...but I don't think I got it all. The algae had really reduced the diameter of the pipe. I've heard of drain "suckers" etc., but am dubious as to how well they work in clearing this type of accumulated slime out. I was thinking some type of chemical treatment....enzymes, etc.?
-
03-23-2012, 06:15 PM #2
I like to come out of the pan into a T then put a short piece of pvc sticking up so the customer can pour a little bleach through the line. I do it on residential installs and walk in coolers.
Dont pour bleach into the tin pan under the coils, just through the drain line.
-
03-23-2012, 07:26 PM #3
Regular Guest
- Join Date
- May 2011
- Location
- CA
- Posts
- 123
-
03-23-2012, 09:01 PM #4
Professional Member
- Join Date
- Sep 2008
- Location
- Cedar Rapids, IA
- Posts
- 473
Putting tablets or pads in the drain pan will also kill algae in the drain line and help it stay clean. Spraying the coil with a coil cleaner at the beginning of the season is also a good pm step. If you have stuff growing in the line then it is also growing in the coil.
-
03-23-2012, 09:28 PM #5
Professional Member
- Join Date
- Jun 2009
- Location
- Garland, TX
- Posts
- 349
Can you not blow it out with CO2?
-
03-23-2012, 11:44 PM #6
Regular Guest
- Join Date
- May 2011
- Location
- CA
- Posts
- 123
Blowing out with c02 or n2 isn't even an option. I flushed it *hard* with 50 psi hot water for several minutes, still didn't remove it.
I will look into the tablets...but dont think i'll ever use them. If water backs up and spills over the cond. pan, the chemicals in the tablet will spill all over the food underneath...which would create a major headache for me (tossing product, questioning product, etc). I can see that type of tablet's use in AC, but not in refrigeration.
-
03-24-2012, 10:09 AM #7
Professional Member
- Join Date
- Sep 2008
- Location
- Cedar Rapids, IA
- Posts
- 473