can you test a screw with a megger? another tech in my company claimes he checked a compressor that was throwing the breaker with a megger against a compressor that was working ok and got the same readings.???????
-
03-21-2012, 11:04 PM #2
You can check any motor windings with a megger.
What makes you think he's lying?UA LU189
10mm, because it's better than .45acp
-
03-22-2012, 07:38 AM #3
dont meg in a vac., and dont over voltage the meg tool with the applied voltage .,
example: 208 motor
meg with 208 not 600 voltno signature
blast'em man blast'em
!!!KILL THE TERRORIST!!!
-
03-22-2012, 08:28 AM #4
Professional Member*
- Join Date
- Jul 2007
- Location
- The Hot South
- Posts
- 860
-
03-22-2012, 08:36 AM #5
Professional Member*
- Join Date
- Aug 2009
- Location
- Prattville,Alabama
- Posts
- 1,102
The same rules apply as to any other motor. But with an RTAC you will probably see lower readings than you would expect. I suspect that has more to do with the POE oil than it does with the motor.
-
03-23-2012, 12:17 PM #6
Yes you can and what were the megger readings???? Was the one tripping the breaker grounded, or pulling LRA?
Sent from my iPhone using Tapatalk
-
03-24-2012, 10:44 PM #7
Professional Member
- Join Date
- Mar 2005
- Location
- Indiana
- Posts
- 125
You can get a bad meg reading on a good rtaa screw compressor. If the compressor has the old style terminals and is rusty under the motor terminals insulators. I have had them go as low a .5 megaohms.
-
03-25-2012, 08:54 AM #8
Well I can try, haha
I know for a fact that not supposed to meg n a vac
As far as my example : we'll that may be wrong example.,
Guess what I was trying to say was if you compressor motor volt rating is 600 volt, not supposed to meg at a higher voltage., am I correct in typing this??

no signature
blast'em man blast'em
!!!KILL THE TERRORIST!!!
-
03-25-2012, 09:17 AM #9
It`s not the voltage that kills a motor. It`s always the current. I haven`t seen an compressor motor killed by megging him. But most compressor manufacturers recommend not to megger with a system in deep vacuum.
"Quality exists, when the price is long forgotten."
Henry Royce
-
03-25-2012, 10:23 AM #10
Professional Member*
- Join Date
- Jul 2007
- Location
- The Hot South
- Posts
- 860
-
03-25-2012, 11:07 AM #11
Professional Member*
- Join Date
- Jul 2007
- Location
- The Hot South
- Posts
- 860
Mlk, after researching this, you are right about not to meg at a much higher voltage than the voltage rating of the motor.
-
03-25-2012, 11:32 AM #12
-
03-25-2012, 02:16 PM #13
i meg everything at 1000 VDC...even 115 VAC motors...no problems. i have also megged motors in 500 micron vacuums without issue...my megger tops out at 0.002 ADC...not gonna hurt anything.
applying line voltage to a motor in a deep vacuum...now that's a youtube video I want to see!Spellin mitsakes bother me.