    rtac/rtaa

    can you test a screw with a megger? another tech in my company claimes he checked a compressor that was throwing the breaker with a megger against a compressor that was working ok and got the same readings.???????

  2. #2
    Join Date
    Aug 2006
    Location
    Columbus Ohio
    Posts
    1,977
    You can check any motor windings with a megger.

    What makes you think he's lying?
    UA LU189

    10mm, because it's better than .45acp

  3. #3
    Join Date
    Jan 2009
    Location
    Not in Iran
    Posts
    992
    dont meg in a vac., and dont over voltage the meg tool with the applied voltage .,

    example: 208 motor
    meg with 208 not 600 volt
    no signature blast'em man blast'em
    !!!KILL THE TERRORIST!!!

  4. #4
    Join Date
    Jul 2007
    Location
    The Hot South
    Posts
    1,207
    Quote Originally Posted by mlkwal1 View Post
    and dont over voltage the meg tool with the applied voltage .,

    example: 208 motor
    meg with 208 not 600 volt
    What??????

    Can you please enlighten us on this????

  5. #5
    Join Date
    Aug 2009
    Location
    Prattville, Alabama
    Posts
    1,757
    The same rules apply as to any other motor. But with an RTAC you will probably see lower readings than you would expect. I suspect that has more to do with the POE oil than it does with the motor.

  6. #6
    Join Date
    May 2011
    Location
    North FL.
    Posts
    180
    Yes you can and what were the megger readings???? Was the one tripping the breaker grounded, or pulling LRA?


    Sent from my iPhone using Tapatalk

  7. #7
    Join Date
    Mar 2005
    Location
    Indiana
    Posts
    148
    You can get a bad meg reading on a good rtaa screw compressor. If the compressor has the old style terminals and is rusty under the motor terminals insulators. I have had them go as low a .5 megaohms.

  8. #8
    Join Date
    Jan 2009
    Location
    Not in Iran
    Posts
    992
    Quote Originally Posted by R123 View Post
    What??????

    Can you please enlighten us on this????
    Well I can try, haha
    I know for a fact that not supposed to meg n a vac
    As far as my example : we'll that may be wrong example.,
    Guess what I was trying to say was if you compressor motor volt rating is 600 volt, not supposed to meg at a higher voltage., am I correct in typing this??
    no signature blast'em man blast'em
    !!!KILL THE TERRORIST!!!

  9. #9
    Join Date
    Feb 2009
    Location
    good old Europe
    Posts
    160
    It`s not the voltage that kills a motor. It`s always the current. I haven`t seen an compressor motor killed by megging him. But most compressor manufacturers recommend not to megger with a system in deep vacuum.
    "Quality exists, when the price is long forgotten."

    Henry Royce

  10. #10
    Join Date
    Jul 2007
    Location
    The Hot South
    Posts
    1,207
    Quote Originally Posted by mlkwal1 View Post
    Well I can try, haha
    I know for a fact that not supposed to meg n a vac
    As far as my example : we'll that may be wrong example.,
    Guess what I was trying to say was if you compressor motor volt rating is 600 volt, not supposed to meg at a higher voltage., am I correct in typing this??
    You are correct that you are not supposed to meg in a DEEP vacuum but I've never heard about not to meg at a higher voltage. As a matter of fact, my megged doesn't go below 500 volts and I meg 230 volt motors all the time.

  11. #11
    Join Date
    Jul 2007
    Location
    The Hot South
    Posts
    1,207
    Mlk, after researching this, you are right about not to meg at a much higher voltage than the voltage rating of the motor.

  12. #12
    Join Date
    Sep 2004
    Location
    Kansas City, Kansas, United States
    Posts
    13,817
    you should set the voltage at twice the rated voltage,
    I almost exclusively work on 480 stuff
    i always meg at 1000 volts.




    Quote Originally Posted by R123 View Post
    Mlk, after researching this, you are right about not to meg at a much higher voltage than the voltage rating of the motor.
    I WILL SELL WORK,GENERATE BUSINESS, GO GET NEW CUSTOMERS!
    YOU SHUT THE HELL UP AND QUIT RUNNING YOUR MOUTH!

  13. #13
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    4,015
    Quote Originally Posted by supertek65 View Post
    you should set the voltage at twice the rated voltage,
    I almost exclusively work on 480 stuff
    i always meg at 1000 volts.
    i meg everything at 1000 VDC...even 115 VAC motors...no problems. i have also megged motors in 500 micron vacuums without issue...my megger tops out at 0.002 ADC...not gonna hurt anything.

    applying line voltage to a motor in a deep vacuum...now that's a youtube video I want to see!
    It's tube brushing season...93% done (39.35 miles of tubing)...only 1,242 tubes to go!

    Original member of the Raccoon Brotherhood.

    EVERYTHING IS AWESOME!!!

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event