Results 1 to 13 of 15
Thread: rtac/rtaa
    Nov 2007
    Mississippi
    rtac/rtaa
    can you test a screw with a megger? another tech in my company claimes he checked a compressor that was throwing the breaker with a megger against a compressor that was working ok and got the same readings.???????
    Ohio
    You can check any motor windings with a megger.
    What makes you think he's lying?
    Not in Iran
    dont meg in a vac., and dont over voltage the meg tool with the applied voltage .,
    example: 208 motor
    meg with 208 not 600 volt
    no signature blast'em man blast'em
    !!!KILL THE TERRORIST!!!
    The Hot South
    Quote Originally Posted by mlkwal1 View Post
    example: 208 motor
    What??????
    Can you please enlighten us on this????
    Not in Iran
    Quote Originally Posted by R123 View Post
    What??????
    Well I can try, haha
    I know for a fact that not supposed to meg n a vac
    As far as my example : we'll that may be wrong example.,
    Guess what I was trying to say was if you compressor motor volt rating is 600 volt, not supposed to meg at a higher voltage., am I correct in typing this??
    good old Europe
    It`s not the voltage that kills a motor. It`s always the current. I haven`t seen an compressor motor killed by megging him. But most compressor manufacturers recommend not to megger with a system in deep vacuum.
    "Quality exists, when the price is long forgotten."
    Henry Royce
    The Hot South
    You are correct that you are not supposed to meg in a DEEP vacuum but I've never heard about not to meg at a higher voltage. As a matter of fact, my megged doesn't go below 500 volts and I meg 230 volt motors all the time.
    Aug 2009
    Prattville, Alabama
    The same rules apply as to any other motor. But with an RTAC you will probably see lower readings than you would expect. I suspect that has more to do with the POE oil than it does with the motor.
    May 2011
    North FL.
    Yes you can and what were the megger readings???? Was the one tripping the breaker grounded, or pulling LRA?
    Indiana
    You can get a bad meg reading on a good rtaa screw compressor. If the compressor has the old style terminals and is rusty under the motor terminals insulators. I have had them go as low a .5 megaohms.
    The Hot South
    Mlk, after researching this, you are right about not to meg at a much higher voltage than the voltage rating of the motor.
    you should set the voltage at twice the rated voltage,
    I almost exclusively work on 480 stuff
    i always meg at 1000 volts.
    Quote Originally Posted by supertek65 View Post
    i meg everything at 1000 VDC...even 115 VAC motors...no problems. i have also megged motors in 500 micron vacuums without issue...my megger tops out at 0.002 ADC...not gonna hurt anything.
    applying line voltage to a motor in a deep vacuum...now that's a youtube video I want to see!