    Anybody ever seen a rtac run in a vacuum? I did for about three min. the other day. I thought it would damage the rotors faster than that.
    Not in Iran
    Quote Originally Posted by socotech View Post
    i believe this is a 134 a machine., this is not a pump down system,. never seen it.;, i would keep ur eye on the txv.,
    no signature blast'em man blast'em
    !!!KILL THE TERRORIST!!!
    Nov 2007
    Mississippi
    Unit was low on refrigerant. Suction isolation valve was leaking.
    The Hot South
    The RTAC shouldn't run in a vacuum and the controls shouldn't let it. We're you seeing this on the DynaView display or your guages? May be a bad transducer.
    Aug 2009
    Prattville, Alabama
    Ummm.... you watched this for three minutes?
    The Hot South
    Was a technician holding in the contactor while pumping down?????or was the chiller running under under its own control?
    Nov 2007
    Mississippi
    Saw this on dynaview then confirmed with gauges. Nobody holding in contactor. Probablly wasnt three minutes, but it was a while.
    The Hot South
    What software version is it running?
    Nov 2007
    Mississippi
    Not sure of the software version. Chiller is 2008 model. Leak was warranty repair.
    The Hot South
    Make sure the software is up to date.
    Nov 2007
    Mississippi
    Has trane been having issues with older version not allowing low press cutout before compressor runs into vacuum?