yep 407c saturation temps are close enough to wing it with electronics im sure
Keep it simple to keep it cool!
-
03-24-2012, 12:27 PM #15
Right on 407c!!!!!!!!
-
03-24-2012, 06:51 PM #16
Professional Member
- Join Date
- Sep 2008
- Location
- A land down under
- Posts
- 285
I would have serious concerns "winging it" with R407c considering the glide when using a DX chiller vessel working off microprocesser staturated pressure/temperature properties of another refrigerant for the chillers safty protection.
I guess you could fit an external low pressure switch for protection but the chillers reliable operation would be compromised.Necessity is the mother of invention
-
03-24-2012, 08:24 PM #17
Professional Member*
- Join Date
- Dec 2004
- Location
- Chicago area
- Posts
- 1,386
I've seen R407c and R22 use the same thermal expansion valves in some cases.
I've seen it a lot on split systems.
The bigger problem on the rtwa will be oil separation capacity. POE oils blend with refrigerant a lot better then mineral oils, which is why no traps are needed on high temp split systems using poe oils.
-
03-24-2012, 11:30 PM #18
Regular Guest
- Join Date
- May 2008
- Location
- austin
- Posts
- 7
Carrier just sent out some info on converting 22 to 407' on a 100 ton machine it's like 17k to convert it. I haven't seen the labor involved . I'm shure if trane would let you convert it would be in the same relm , may want to replace the machines. Don't think it's worth the cost to convert. I don't remember what they said about capacity. Dozed off during that meeting