    KW cooling or KW electrical consumption

    Hello all, I believe I am limited to posting here as I am such a newby..

    Anyway, if I have a 3.5ton airconditioner it will use approx. 6KW of electricity when running.

    3.5tons is 42,000 BTu which equates to (42,000 / 3412 = 12.3KW)

    Why is my KW cooling different to the KW consumed and what laws/rules should I be looking up so I understand this better.

    Electrically I am squared away but this problem has always just been out of my reach...

    Thanks for any help you can offer to guide this newby to what is probably the most obvious thing (when you know where to look)

    Cheers
    Poccur

  2. #2
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,671
    Post Likes
    It is easier, work wise, to move heat than to create it.


    The formula you are using is a direct electrical relationship of kw to BTUs. This would only be accurate for using an electric heating appliance.

  3. #3
    Join Date
    Jan 2001
    Location
    Nebraska
    Posts
    319
    Post Likes
    If you are a HVACR student or a rookie, you have arrived at the point where you need to research COP (Coefficient of Performance) and EER (Energy Efficiency Ratio).

    PS: Get your pro status and ask your questions in a Pro catagory and you can get more details in the discussions.