Results 1 to 10 of 10
    Dec 2010
    new jersey
    sight glass or moisture indictor? is the question.
    I believe I read once that, on a hill rack they used to use a sight glass,but, it is NOT inline w/ the liquid line, but, instead it has 2 -1/4 " lines that attach it to the side of the liquid line.
    Is it true that this style of piping the s/g it is used solely for moisture indicating only and NOT for determining liquid content.
    I can try and dig out my old Hill books, but I'm trying to avoid that If possible.
    California
    Dec 2010
    new jersey
    yes, exactly what I mean...
    Thanks, Phase Loss.
    Dec 2011
    is it a 3/8 line? thats how they did it way back,something to look at and a lot less than a saddle type.
    Columbus Ohio
    When you start getting into the large pipe they use the "bypass" to cut down on cost. Can you imagine the price tag on a 2" moisture indicator fitting?
    It is used solely for moisture indication not as a liquid indicator.
    UA LU189
    10mm, because it's better than .45acp
    May 2008
    brooklyn ny
    yes you are right those hill rack have a sight glass on the liquid line that is a 1/4ins line connected to the shightglass at the side of liquid line so that a mositure indicater did not know that throught that was for liquid.
    Cedar Rapids, IA
    Quote Originally Posted by zw17 View Post
    If installed as recommended it will indicate liquid. The turbulence caused by the small lines and curves will cause liquid with low subcooling to flash in the glass more than the relatively open path in the larger pipe.
    May 2008
    brooklyn ny
    but in the newer rack they do have sightglass in the liquid line weather it 7/8 1 1/8
    Dec 2011
    sightglasse's are nice to look at but subcooling is the best way to check charge.
    it will indicate solid column as well
    Keep it simple to keep it cool!