Results 1 to 13 of 18
Thread: Why has it never cooled well?
-
03-20-2012, 08:05 PM #1
Why has it never cooled well?
And why did it fail? Comp permanently open at IOL.
Changing out a 3 ton Goodman system in an upstairs lake house and when I removed the condenser, I noticed the armaflex had a crease in it and it moved easily. Found a major kink in the line and will have to cut up the wall to get to good copper. No way to replace this copper without major retrofitting (No attic and up stairs between floors).
Then inside with the air handler out, I saw another crease in the armaflex- yep- another kink.
Been like this since day one. Customer said it never cooled much. Amazing it lasted this long.

At condenser;

At air handler;


-
03-20-2012, 08:12 PM #2
Your unit and the neighbours is way up of the ground.
You trying to keep them away from cooper theives.
Dog urination.ENJOY THE RIDE
-
03-20-2012, 08:19 PM #3
-
03-20-2012, 08:26 PM #4
Professional Member*
- Join Date
- Sep 2005
- Location
- North GA
- Posts
- 17,316
-
03-21-2012, 12:29 AM #5
Professional Member*
- Join Date
- Dec 2007
- Location
- Middle TN
- Posts
- 57
-
03-21-2012, 03:54 AM #6
OSHA would love you for that duct jack stunt.
UA LU189
10mm, because it's better than .45acp
-
03-21-2012, 09:04 PM #7
Thats a 1,000 lb capacity lift with legs that outrig to 5' wide.
Has the aluminum forks that weight 40 lbs a piece and a 3/16" metal platform bolted down. You won't find a more stable way to get it up there. It doesn't move. I don't see how it is a stunt.?
It's what it's made for.

http://www.genie-lift.com/index.cfm?...traddle%20Base
With the options- mine is about $3,800.00 -
I found it on craigslist being used in a weather controlled warehouse for $700.00.
-
03-21-2012, 09:53 PM #8
1) I cannot see the outriggers but we can assume they are out?
2) I don't see how the load is secured to the lifting device.
3) The lift is located on unstable ground, needs plywood under it to be considered solid ground.
This is just the three I can find within a minute of looking at this pic.
Not busting your balls, just playing devils advocate in the hopes of keeping you safe.UA LU189
10mm, because it's better than .45acp
-
03-21-2012, 10:34 PM #9
-
03-21-2012, 11:41 PM #10
Professional Member*
- Join Date
- Jun 2008
- Location
- Pontotoc, MS
- Posts
- 79
Still consider myself a newbie, but I see things done like this all the time. We wonder why people think or trade is crooked. Drives me crazy, what ever happened to quality workmanship, that's what made America great. Not this " Good enough for government work" crap. If you wouldn't do it on your mama's unit, then don't do it to someone else's. Just my 2 cents.
-
03-22-2012, 12:19 AM #11
Professional Member*
- Join Date
- Sep 2005
- Location
- North GA
- Posts
- 17,316
GA-HVAC-Tech
Galatians 2:20-21; Colossians 1: 21-22 & 26-27; 3:1-4; Romans Ch's 5-6-7-8
2 Chronicles 7:14
Quality work at a fair price with excellent customer service.
-
03-22-2012, 06:14 PM #12
I understand what your saying.
The wheels are setting on ply squares that have holes in them for the wheels to lock into- you can't see that except just to the left of the new a/c on the ground.
No- it isn't tied down and maybe it should be, but as hard as it is to slide the condenser, my concern is only the lift falling over.
Since it is on level ground and the ground is hard packed, I didn't extend the legs. I couldn't extend the leg to the left anyway.
So far this is maybe the 6th one and some were setup on what would be considered unsafe ground, but if you take your time to set it up, you can make it without a hitch. Most important is to have it level.
If it could fall in any direction that would damage property, I would rope tie it in some way to prevent that.
You should have seen the one we could rent from Trane- a ratchet type lift that swayed in the wind and you had to ratchet it as you went up with it on a ladder.
-
03-22-2012, 06:22 PM #13
Probably kinked after lineset was roughed out. Landscapers are notorious for this. Should have been caught before install though......