    Stuck txv

    So in ac my high side pressures were pretty normal, but my low side was about 30 psi (410 a system). All my spider legs are freezing up and so I took the bulb off of the suction and put a wet towel on it then I went back up to my guages and my low side was still sitting on 30psi, not hunting at all. I diagnosed a stuck txv. Do you agree?

  2. #2
    Join Date
    Mar 2010
    Location
    Chapel Hill, NC
    Posts
    52
    wet, warm towel that is.

  3. #3
    Join Date
    Jul 2006
    Location
    NW burbs of Detroit
    Posts
    6,058
    sounds like to me

  4. #4
    Join Date
    Nov 2001
    Location
    east kansas
    Posts
    8,038
    Yes. When you purged your high side hose, was there a lot of liquid.
    Beware of advice given by some guy on the Internet.

  5. #5
    Join Date
    Mar 2010
    Location
    Chapel Hill, NC
    Posts
    52
    yeah there was actually. Tons. the remnants of what the evaporator was storving for I presume.

  6. #6
    Join Date
    Feb 2003
    Location
    Wichita Ks
    Posts
    1,507
    what was your subcooling?

  7. #7
    Join Date
    Mar 2010
    Location
    Chapel Hill, NC
    Posts
    52
    didn't check superheat or subcooling due to the fact that I couldn't get the txv to hunt. Probably should have but didn't. I can tell you that the high side was pretty much spot on for what Lennox said it should be.

  8. #8
    Join Date
    Feb 2003
    Location
    Wichita Ks
    Posts
    1,507
    your subcooling would have told you if you was stacking freon in the condenser or low on gas.

  9. #9
    Join Date
    Jul 2006
    Location
    NW burbs of Detroit
    Posts
    6,058
    Well, I would agree that while this is an obvious restriction based on the info you provided, a SH and SC check should always be performed.

  10. #10
    Join Date
    Mar 2010
    Location
    Chapel Hill, NC
    Posts
    52
    I agree. That is only the second stuck txv that I have come across and will remember to do a sh and sc check next time and will in fact do one on this unit before I begin the work of changing it. I would think that the superheat would be more important to the diognosis than the subcool, am I wrong?

  11. #11
    Join Date
    Aug 2006
    Location
    Ohio
    Posts
    2,094
    I always use a cup of warm water and ice water to see how the TXV reacts but I suppose a warm/ice cold wet towel would work and be a little bit easier to handle.

  12. #12
    Join Date
    Mar 2010
    Location
    Chapel Hill, NC
    Posts
    52
    Quote Originally Posted by freonrick View Post
    your subcooling would have told you if you was stacking freon in the condenser or low on gas.
    oh, right on. good point. Thanks.

  13. #13
    Join Date
    Jul 2006
    Location
    NW burbs of Detroit
    Posts
    6,058
    Quote Originally Posted by Bigdtown View Post
    I agree. That is only the second stuck txv that I have come across and will remember to do a sh and sc check next time and will in fact do one on this unit before I begin the work of changing it. I would think that the superheat would be more important to the diognosis than the subcool, am I wrong?
    No, the SC is most important in this case...the evap is going to be starved and SH will be high...

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Comfortech Show Promo Image

Related Forums

Plumbing Talks | Contractor Magazine
Forums | Electrical Construction & Maintenance (EC&M) Magazine
Comfortech365 Virtual Event