Results 1 to 7 of 7

Thread: Dunham Bush

  1. #1
    Join Date
    Sep 2011
    Posts
    31
    Post Likes

    Dunham Bush

    Hello

    I am in a service which is a unit Dunham Bush can support me with some information bulletins Service Manual appreciate any support ACHDX250 Model R-407C-6QP

    Regards

  2. #2
    Join Date
    Aug 2006
    Location
    Ohio
    Posts
    2,571
    Post Likes
    Get your post count up and become a verified pro member.

    Read the rules about this not being a DIY site.

  3. #3
    Join Date
    Jan 2009
    Location
    Not in Iran
    Posts
    1,198
    Post Likes
    Quote Originally Posted by kaltebajio View Post
    Hello

    I am in a service which is a unit Dunham Bush can support me with some information bulletins Service Manual appreciate any support ACHDX250 Model R-407C-6QP

    Regards
    other than supply u with a manual., i dont understand ur lingo
    no signature blast'em man blast'em
    !!!KILL THE TERRORIST!!!

  4. #4
    Join Date
    Sep 2011
    Posts
    31
    Post Likes
    Thread Starter
    Recently come to a service which has 1 unit Dunham bush which has damaged the 2 I have no Historal a compressor this unit can not find the manual for this unit HD1468641

    Regards

  5. #5
    Join Date
    Mar 2012
    Location
    Miami Florida
    Posts
    16
    Post Likes
    Man your spelling is horrible. The company I worked for the past 4 years was a DB dealer and I have worked on many of them. DX and Flooded but mostly flooded chillers with the vertical screw compressors.. That model number that you are giving out does not ring any bells. I guess that it might be a new system or a DX system that I have not seen. What is your problem anyways?

  6. #6
    Join Date
    Jan 2009
    Location
    Not in Iran
    Posts
    1,198
    Post Likes
    Quote Originally Posted by manny2326 View Post
    Man your spelling is horrible. The company I worked for the past 4 years was a DB dealer and I have worked on many of them. DX and Flooded but mostly flooded chillers with the vertical screw compressors.. That model number that you are giving out does not ring any bells. I guess that it might be a new system or a DX system that I have not seen. What is your problem anyways?

    It's not his spelling, it's his putting a question and answer together., maybe not American decent,?
    no signature blast'em man blast'em
    !!!KILL THE TERRORIST!!!

  7. #7
    Join Date
    Sep 2011
    Posts
    31
    Post Likes
    Thread Starter
    My English is horrible try to write less
    2 units ACXI250 Dunham Bush no history
    it recovers R-407 4 systems
    Leak check
    Vacuum to 500 microns
    charging by weight R-407
    Sistemas #1 136 kgs
    Sistemas #2 164 kgs
    Amper Plate
    Sistem #1 180 Amps
    Siatem #2 214 amps
    Cutting points high at 370 psi for 30 psi low
    Change for High Low 50 psi 320 psi
    System 1 leader compressors
    Pressure differential in water at 10 psi

    Program

    LV WTR SP A=45 B=0.8
    Lead A= 2.0 B=1.0
    Ramp Up A=0.4 B=30.0
    Pulse WTH A=20.0 B=1.0
    Dead Band A=5.0 B=3.0

    Working
    54F LVT 60F
    C1 Succ 70 psi Des 261 psi
    C2 Succ 85 psi Des 275 psi
    Superheat 8F sub cooling 9F
    Temp Amb 75F all fans operating both systems
    C1 Desc Temp 165F
    C2 Desc Temp 155F
    Ampers Measured
    Sistema #1 166 amp
    Sistema #2 190 amp
    I searched newsletters manuals compressors for loading and unloading de slide
    Both the units of the system 2 will not exceed 15% FLCP systems 1 to 100% in FLCP

    Question

    That is the FLCP???
    Would have to operate at 100% both FLCP??
    I have to make a change in program for 100% load FLCP systems # 2?
    Will pressure drop graphs for this unit and review appropriate galonajes

    I appreciate your comments Regards