03-15-2012, 03:06 PM #1
banned by Admin
- Join Date
- Dec 2010
- Location
- New Orleans
- Posts
- 1,012
7.5 ton unit need help
I have a restaurant cust. that has an above t-bar air handler [Old] no name plate left. TXV slant coil with a trane 7.5 ton condenser. The problem is air flow. When system installed the installer hooked a 16 inch return to to air handler which is way too small. The compressor was changed about one yr ago, before I inherited. My question is; would disconnecting return flex duct and using t-bar ceiling as return, increase the air flow? I believe it would, but before I dive in would like some feedback please.
-
03-15-2012, 04:23 PM #2
Professional Member*
- Join Date
- Aug 2007
- Location
- Northern VA 38 degrees N by 76 degrees W
- Posts
- 3,251
-
03-15-2012, 09:42 PM #3
-
03-15-2012, 09:54 PM #4
Being that it is a restaurant what does it have in place to run 365?
Hot gas? Auto reset Freeze stats on the Evap? Condenser fan control? etc?
-
03-16-2012, 08:34 AM #5
banned by Admin
- Join Date
- Dec 2010
- Location
- New Orleans
- Posts
- 1,012
Freeze stats on coil, no smoke alarm in return. I think there might be a prob with a restriction at txv screen, I have replaced driers already and pressures way off. There does exist a smoke detector laying on t-bar??? who knows why, Remember New Orleans is the Big Easy and probably never inspected- you should see this place, terrible.
-
03-16-2012, 08:40 AM #6
Regular Guest
- Join Date
- Feb 2012
- Location
- Upstate SC
- Posts
- 84
An additional question that I would ask is how tight is the air space above the ceiling and is this a one story? You have the potential for creating a humidity problem given your location.
-
03-16-2012, 09:20 AM #7
banned by Admin
- Join Date
- Dec 2010
- Location
- New Orleans
- Posts
- 1,012
No two story and I would add return grills. Even though I know there exist a return air flow problem I am going to inspect txv screen and try to adjust the txv to get suction pressure up.
-
03-17-2012, 09:00 PM #8
I would drop a bunch of open top t-bar diffusers in to pull from the conditioned area, using the ceiling as a giant plenum. That would eliminate the humidity issues because it would still be pulling from the "comfort" area.
The only decision in life is to decide what to do with the time given to you
-
03-17-2012, 09:49 PM #9
Professional Member*
- Join Date
- Dec 2003
- Location
- Citrus County, Florida
- Posts
- 1,252
If the area above the ceiling is not sealed, I believe you will be pulling all sorts of garbage and humidity into the return. Plenum returns are not advised. Why not add the proper ductwork? You short on return. Cure the airflow problem and then adjust the TXV and charge. What is the static pressure? I'll bet the return is out of sight.
Doug
-
03-19-2012, 08:15 AM #10
banned by Admin
- Join Date
- Dec 2010
- Location
- New Orleans
- Posts
- 1,012
-
03-19-2012, 08:41 AM #11
If you make a plenum return along with what everyone else mentioned you will increase the conditioned space area. Can the equipment handle the load?