    I'm checking up on my contractor so I want to make sure the heat pump is proper tonage.
    My home is 2060sq ft. It is two story with dual pump/air handlers. I don't know the tonage on the pump but the air handlers are 2 ton units. The pumps are Trane XE-1000's and the air handlers are Trane TWG025A's(2 ton according to Trane's website).

    Your help is appreciated.

  2. #2
    Join Date
    May 2000
    Location
    Monmouth Junction-NJ-USA
    Posts
    6,125
    Post Likes
    Get the model #s of the outdoor units. If he is putting in two 2 ton units it sounds oversized. Do a load calculation and you will know what the requirement is.
    If you really know how it works, you have an execellent chance of fixin' er up!

    Tomorrow is promised to no one...

  3. #3
    Join Date
    Jun 2001
    Location
    New Jersey
    Posts
    1,565
    Post Likes
    Try http://www.HVAC-Calc.com for residential systems. Using the square footage method can get you in trouble. It is worth the $39.00

  4. #4
    Join Date
    Jan 2002
    Posts
    10
    Post Likes
    Thread Starter
    I'll get the model# and post tonight. I don't know how to do a load calculation.

  5. #5
    Join Date
    May 2000
    Location
    Monmouth Junction-NJ-USA
    Posts
    6,125
    Post Likes

    Thumbs up

    You get the Hvac-Calc program which is self explanatory and you will know how to do a load calc. It is really easy and worth the effort. A lot of HO's from this forum have done it.
    If you really know how it works, you have an execellent chance of fixin' er up!

    Tomorrow is promised to no one...

  6. #6
    Join Date
    Jan 2002
    Posts
    10
    Post Likes
    Thread Starter
    I was hopeing someone could help me without my spending $40 right now. I'm a bit tight with other expenses now.

  7. #7
    Join Date
    May 2000
    Location
    Monmouth Junction-NJ-USA
    Posts
    6,125
    Post Likes
    $40.00 is certainly cheap insurance for the type of investment you are making. A mistake can cost you thousands down the road, not to mention the discomfort.
    If you really know how it works, you have an execellent chance of fixin' er up!

    Tomorrow is promised to no one...

  8. #8
    Join Date
    Jan 2002
    Posts
    388
    Post Likes
    Originally posted by rayr
    $40.00 is certainly cheap insurance for the type of investment you are making. A mistake can cost you thousands down the road, not to mention the discomfort.
    As a homeowner with no tech. experience, I totally agree with rayr, and recommend you suck up the $39. I did, and honestly, it was a snap. I actually compared notes with the load calcs that 2 contractors had done and found that it was right in the ballpark (mine was actually off a bit because I didn't measure a couple of things correctly). But, in the end, I understood exactly why the contractors were recommending the size units they were recommending. Turns out that my upstairs system was oversized and there were at least 2 guys who simply said "Oh, you have a 2 1/2 ton unit now, so we'll need a 2 1/2 ton unit to replace it" when, in fact, my upstairs needed just a shade over 1 1/2 tons. Saved me some $$$.

    So, IMHO, forgo your morning coffee and paper for a couple of weeks if you have to. $39 could save you thousands.

  9. #9
    Join Date
    Jun 2001
    Location
    New Jersey
    Posts
    1,565
    Post Likes

    Angry

    I may be getting out of line here, but leedesert, I believe you will try to give your contractor a hard time. I smell something fishy here.
    $39.00 is not a lot of money to pay to get the results needed for your home.
    HVAC is a big investment for your home. You want cheap, you are going to get cheap.
    I personally believe you want to see if you are getting ripped off. I can understand that if that is your thought. Did you get referrals from friends or relatives about an HVAC contractor? If you did let him do his job. You'll be back on this forum crying later.

  10. #10
    Join Date
    Apr 2001
    Posts
    621
    Post Likes
    Originally posted by leedesert
    I was hopeing someone could help me without my spending $40 right now. I'm a bit tight with other expenses now.
    You can't accurately size hvac equipment in a discussion forum and there is no sq footage "rule of thumb" that sizes correctly either.

    If you're too cheap to spend 40 bucks for a load calc, save it now, but you'll spend a lot more than that on the oversized equipment you'll get stuck with in your install. You'll also pay for it every month in higher utility bills and shorter equipment life from short-cycling compressors.


  11. #11
    Join Date
    Sep 2001
    Location
    richmond,va.
    Posts
    152
    Post Likes

    Cool WHY CHANCE IT

    A load calculation needs to be done. That is the only way of knowing what your house needs. HVAC-CALC. is the only way to go. Is this a new home or existing. Ask the contractor for the load calculation for your house. Thirty nine dollars is a small price to pay for peace of mind.

  12. #12
    Join Date
    Jan 2002
    Posts
    10
    Post Likes
    Thread Starter
    Thank you for your suggestions but to be quite honest, there are people out there willing to help someone without making someone spend $40 on a program he will use once. I was hopeing to find people like that here.

    I just checked up on my pumps and they are each 2 ton unit (24,000 BTUH).

    My downstairs is 1250sq ft and upstairs is 810sq ft.

    If anyone can tell me if this sounds about right for the units they installed please reply, I appreciate any comments that help.

    I may be getting out of line here, but leedesert, I believe you will try to give your contractor a hard time.
    You're right, you're out of line. I just want to make sure the most used appliance in my house is done right. I have about 1 more week to check on these items and I just don't have $40 to spend.

    I have noticed that this sites sole advertiser is HVAC Calc. Very interesting.

    If someone can offer advise besides "buy the program" I'll appreciate it.

  13. #13
    Join Date
    Aug 2000
    Location
    St. Petersburg, Fla. U.S.A .
    Posts
    35
    Post Likes
    Hi leedesert - Yep, sounds like the right size to me. 2 tons is exactly what you need.

    Glad we could be of help.

  14. #14
    Join Date
    Apr 2001
    Posts
    621
    Post Likes
    Originally posted by leedesert
    ... I just want to make sure the most used appliance in my house is done right.
    I've got news for you, you're not going to get it "done right" by sizing it on the internet. Anyone who doesn't get a load calc done, especially with HPs, is a fool.

  15. #15
    Join Date
    May 2000
    Location
    Monmouth Junction-NJ-USA
    Posts
    6,125
    Post Likes
    If you didn't plan on taking the advice of people who have done this for a living for decades, why did you bother to ask?? Keep asking around and sooner you will hear the answer you want to hear. LOL
    If you really know how it works, you have an execellent chance of fixin' er up!

    Tomorrow is promised to no one...

  16. #16
    Join Date
    Sep 2001
    Location
    richmond,va.
    Posts
    152
    Post Likes

    Cool

    Again I recommend asking your contractor for the load calculation. We as a group do want to help. Better to be mad at your contractor than the people on this web site. If you have to check-up on your contractor sounds like you have the wrong contractor. I don't think anyone is getting any residuals from recommending Hvac-Calc. I use it and it works.

  17. #17
    Join Date
    Jan 2002
    Posts
    10
    Post Likes
    Thread Starter
    ok, I'll contact my builder to get the load calculations. I'm sorry if I got a bit short but Charlie's comment rubbed me the wrong way.

    I guess what I'm looking for is if the size match sounds close to correct. I know you can't be exact but I don't want to waist a lot of time and irritate my contractor with having to look up information like this if everything is ok. I'm reconsidering buying that program on my credit card so don't think your advice is not heard. Thanks for your inputs, even those I didn't like.

  18. #18
    Join Date
    Sep 2001
    Location
    richmond,va.
    Posts
    152
    Post Likes

    Cool

    We understand your situation. Let us know how everything turns out. Enjoy your new home.

  19. #19
    Join Date
    Oct 2001
    Posts
    6,071
    Post Likes
    The problem here, which no one has explained fully, is that we can not possibly even guess closely with the information you have given us here. If your house is a typical construction, located in Oklahoma, with no shade, on the south west side of a hill, two four-ton units may or may not do it, (I have 5 tons on 2400 sq ft) depending on how much glass is present, how much insulation in ceiling and walls, what kind of windows and doors, vinyl siding or brick, how many occupants in house, what setting do you like your cooling set on, do you have attic ventilation (power or natural?)

    On the other hand, if your home is located in Wisconsin, and of any recent vintage, 4 tons is over sized. There are W-A-Y too many variables for anyone here to make a semi-accurate guess.

    Now, to address the other problem here. When someone shows up at your front door, or calls you on the phone, and asks you a question, you can't help but wonder why they want to know. So, you base your response on the EXACT wording of their question, and the attitude with which they asked it. Most of the guys on this web site are contractors. You began your question by saying,
    " I'm checking up on my contractor so I want to make sure the heat pump is proper tonage. "
    You might as well have said, "I don't trust contractors, you all lie and steal, so tell me if my contractor is lying or stealing." No, that is not what you said, that's what most people here heard you say. Then, to add injury to (perceived) insult, you refuse to spend $40 to perform a load calculation that would be accurate and remove all your doubts. The man who created HVAC-Calc owns this web site, and pays the considerable fees involved in hosting and moderating a web site this size. He is, by default, the only advertiser. But, we don't get paid for selling you the product. If we did not believe it was; by far, the greatest product of it's kind on the market, we'd give you some other advice.

    So, as a design engineer, what is it I'm trying to say? Download the program, and by this time tomorrow, you'll not only know exactly what your load should be, you'll understand why your load is that much (or that little) and where changes to your home might benefit you most.

    Sorry if we came across a little strong, we just perceived that you came across that way. If you'd like to give us some more information about the details I mentioned, someone here can make a semi-close guess at your load, but it's still only a guess.

    Goodluck with your house. Let us know what you decide to do.
    Hindsight is NOT a plan!

  20. #20
    Join Date
    Nov 2000
    Location
    Memphis TN USA
    Posts
    6,969
    Post Likes
    The first step is check your contractors refferences. If he seems like a duck, he is probably a duck. If he has done good work for your friends and people you trust he will do good work for you. Don't buy the program if you don't want. Many people get a good feeling from getting in on their own job. The peace of mind from doing the relatively easy calculations yourself, is worth $40. AC systems cost a good deal of money, peace of mind is priceless.

Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •